HOW TO CALCULATE EHV CABLE SIZING?
Answers were Sorted based on User's Feedback
Answer / ram
Use manufacturer table.
1st step:Calculate the FLC.
2nd:Calculate the Voltage drop.( If It is more than 5%)
chose higher size.
3rd step:Calculate fault Current for the system and see
cable short circuit withstand.
| Is This Answer Correct ? | 12 Yes | 4 No |
Answer / hanumantha reddy
i belive this is currect thank you for your information
| Is This Answer Correct ? | 2 Yes | 2 No |
what happend when 230v dc motor we supplied a 23v ac supply
I am having a DG set.The 415 V from Generator is step up to 460 v and then the same is used for Induction furnace. before Step up, I am connecting LT load to my factory use. When Induction furnace is in service from DG, when i try to start a motor, the generator is tripped.Please tell me the reason.
the winding of Gen and Motor is star or in delta ??? and why
what is MC 61 relay
how to avoid electrical shock how capacitor store charges wat are the speed control of induction motors state faradays law flemings left hand rule what is rotary converter wat is transmission and distribution what are the sources of energy abrevation of acb,vcb,sf6,igbt what is output equation of transformer which test copper iron and iron loss are calculated what is eddy current draw a single line diagram (10 marks) draw direct online starter(10 marks)
1)What are the proccedure of initial charge of 100AH lead Acid battery bank 2)whether discharge test is reqd ? if it is rqd why, how 3)what are the discharge critieria (volt/cell or sp.gravity/cell
What is the difference between earth fault protection of motor feeder with CBCT and Without CBCT ?
1 Answers Enmas, Michelin, Reliance,
Differentiate between Zero and Negative sequence current
When we have earthing mesh or underground earthing network in industrial plants, weather we have NT-S or NT-C-S kind of earthing system, so eventually weather we must use 4 or 5 wire in 400 volt level (For example 3×150+70 mm2 or 5×150 mm2) in this connection I would like to know exactly the paragraph of IEC or IEEE number
How line capacitance & line inductance varies with increase in height tower.
what purpose to use excaiter in DG.?
Sir we have 12.5 MVA(110/11KV) transformer (Y-Y) connected,which tripped showing earth fault,when we charged transformer it stood OK ,but on connecting 11 KV feeders it tripped showing earth fault.our service engineers found that the B phase and R phase phase connecting to neutral broken from HV OLTC(on load tap changer),and R phase and Neutral is ok.Dissolved gas analysis shows that accetline content is high,tan delta value is 12.My dout is it is an internal fault of transformer,why REF or diffrential relay is not acted?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)