if a dp transmitter has range 100 in H2O and flow is 20mmcf
and if the flow is changed to 25 mmcf then what is the
formula to determine new range of transmitter
Answer / carl_ellis
design max flow rate = 20 mmcf
design max DP = 100 in H2O
new max flow rate = 25 mmcf
new max flow rate = ?
The max flow rate increases by 125% over the design max flow
rate:
25/20 = 125% increase
DP calculations are done in normalized percentages. 125% = 1.25
To calculate the corresponding DP at a max flow rate 125%
higher than the original, where X = DP
sq rt of X = 1.25 (square root of normalized percentage
of DP)
X = 1.25^2 = 1.562
1.562 = 156.2% (work in normalized percentage)
156.2% of 100 inH2O = 156.2 in H2O at a max flow rate of 25 mmcf
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
How we can re-range the DP transmitter, range is -0.5 to 2.0bara. new range is -0.5 to 5 bar
I have installed a RTD whose length is 2250mm(RTD stem length), but it's upper 200 -250mm is out of the reactor, and this upper 200mm stem is surrounded by atmospheric temp. And the lower portion i.e. 2000mm is in contact with the measuring fluid, then does the final measuring temp. Gonna change as the upper 200mm RTD stem is out of reactor?
1 Answers Process Control Technologies,
why use to 250 ohm for hart protocol and why hart communicator not communicate without 250 ohm
WHAT IS DOPPLER EFFECT? WHERE IT IS APPLIED?
sir,would you please send me the Hindustan petroleum corporation limited papers(HPCL).my e-mail ID is ujjwal_sharma1983@yahoo.com
what do you mean by CJC (cold junction compensation).?
What skill/s does the Instrument Technician has?
What is the difference between local indicator(flow) and flow indicator?
why we use sensing type(NPN)on a vibration monitring system not a (PNP)sensing type
Coal mill Instruments Equipments for cement plant And process diagram ?
Hi Frnds , If Suppose 1 Pair cable of 1.5 sq mm is used for Transmitter and instead of 1.5 sq mm if i used 0.5 sq mm cable will the resistance change will occur and does it affect our transmitter reading. plz mail ur answer to ntnkamble@gmail.com plz immediately mail ur reply
how to use K thermocouple instead E- type without compesation cable
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)