if a dp transmitter has range 100 in H2O and flow is 20mmcf
and if the flow is changed to 25 mmcf then what is the
formula to determine new range of transmitter
Answer / carl_ellis
design max flow rate = 20 mmcf
design max DP = 100 in H2O
new max flow rate = 25 mmcf
new max flow rate = ?
The max flow rate increases by 125% over the design max flow
rate:
25/20 = 125% increase
DP calculations are done in normalized percentages. 125% = 1.25
To calculate the corresponding DP at a max flow rate 125%
higher than the original, where X = DP
sq rt of X = 1.25 (square root of normalized percentage
of DP)
X = 1.25^2 = 1.562
1.562 = 156.2% (work in normalized percentage)
156.2% of 100 inH2O = 156.2 in H2O at a max flow rate of 25 mmcf
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
Can SmartPlant Instrumentation be used in a concurrent engineering environment?
Somebody tell me in what way i need to prepare for csio pgrpe(adv instrum eng)interview?what all the quest can i expect?
I am pujita completed Electronics and Instrumentation Engineering.As a fresher i am going to attend the interviews.Could anybody guide the topics/questions covered mostly in interviews.
What is the use instrument barriers? Can you give me review materials about this?
Define all the process Variable and state their unit of measurement. ?
What is the Difference between E/P Positioner and I/P positioner in a control valve? In which applications the respective positioners are used in?
If a flow transmitter (magnetic type FT) that can measure flow and temperature, then why in some industries people use flow transmitter and temperature transmitter in the same line 1 after another? Even after 1 single flow FT is capable of measuring flow as well as temperature.
1 Answers Process Control Technologies,
Name some of the common protocol use in automation.
Explain an adaptive / self-tuning controller’s major draw card.
why we are using drum level control valve air to close?
If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?
8 Answers Bharathi Cement, Titanium,
I want to use 1/2 inch SS316 tube in my high pressure & temperature (64 kg/cm2 & 500 deg C)after condensate pot in pressure tranmistter. 1) Is it possible to use 1/2" ss316 tube in high pressure and temperature line. Tube manufacturer is local vendor. 2)On sarting the plant, We need to do system fluse that time condesate is not in the condesate pot so steam is directly contact with the tube. We have no exact calculation to know our tube is ok or nor at this time. pleae,reply.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)