It depends on how much voltage the field transmitter needs to operate and the total loop resistance of the loop circuit .
Every 2 wire loop powered transmitter has a specification for the voltage required to drive a given loop resistance. Sometimes that is a formula, sometimes a load line graph, sometimes a statement like "minimum liftoff voltage is 17.7V", or rarely, a vague statement of maximum loop resistance (common with active analog outputs, rare with loop powered transmitters)
Excessive wire resistance in a 2 wire loop powered transmitter circuit can affect the operation by
- preventing the transmitter from turning on and operating
- allowing partial operation at lower current outputs, but failing to operate at higher current outputs. That failure can be either an output that just never exceeds a certain value or a transmitter that cycles on-off-on-off an never initializes.
If there is sufficient voltage to run drive the total loop resistance, then the transmitter could function normally.
You need to calculate the wire resistance over its total wire run length (out and back) and know what the receiver's analog input resistance is. Then look up the specification for how much resistance the transmitter's can drive and see whether your loop resistance is lower than the maximum.
Carl Ellis
Measure First
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the difference between HMI and SCADA and MMI
what is the difference between active & reactive power?
Pressure tx shows 1 mbar but we need 1000 mbar at this process condition .. how can we sort it out .
can we replace a slot sensor (inductive type) with limit switch (potenial free contact / no-nc type).
why does mA signal preferred for signal transmission?
Technician A says that a fuel tank sending unit will have a high resistance only when the tank is full. Technician B says that its resistance when the tank is full depends on whether the sending unit is designed for use with a bimetallic gauge or with a magnetic gauge. Who is correct?
What care will you take in the installation of control valves,SCADA,DCS and FOC in Oil and Gas Project?
HOW THE ORIFICE & PRV SIZING BE HAPPENED -- EXPLAIN IN BRIEF
what is intrinscily safe system and where we use?
Can anybody explain about wellhead control system.
What is calibration?
what is meant by nuclear collector?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)