How to check vortex flow meter is in good condition while
we do not having calibration setup?
Answers were Sorted based on User's Feedback
Answer / krishna reddy
Let me know first which make you have.
Instrument have min and max ranges on its name plate.
So wiht multimeter you can check 4-20ma of flow meter.It
must be 4 ma if flow is zero and 20ma if flow is max range.
supose your flow mete got 100L/hr.
for 4ma flow should be 0 L/hr
8ma - 25L/hr
12ma - 50L/hr
16ma - 75L/hr
20ma - 100L/hr
Like this you can check.
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / amit
U can do the cold test by checking the sensor.It has piezo
sensors in symetrical manner. U can check both piezo
sensor by checking the capacitance. If capacitance is
accordance with size means sensor is OK. same way u can
check temp and pressure sensor(by checking the resistance)
if it has.This way u can check the healthiness of the
sensor. If u want to check the response of sensor, u can
give little vibration to the sensor by hammering on it and
check the response on transmitter. U cannot directly check
the calibration for flow on field itself.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / tuhin
@soumil: no hp and lp side exist in vortex flowmeter. Vortex
principle is different.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / saumil
In this meter hp or lp any one side we isolate line valve and check zero if it is ok then meter is ok
| Is This Answer Correct ? | 1 Yes | 3 No |
can we copy the software from a transmitter using hht(hart 275) ?
Im working in a shopping center, it is also hotel and office building, two towers exactly and someone is proposing a PLC control for the HVAC system, but Im thinking of a DDC control system. in this case what is the difference between PLC and DDC control?
any thing about plcs?
In apron feeder how TPH is calculated?
How many types of sensors are used in instrumentation & what are names
what is the si unit of pressure?
6 Answers HTA Instrumentation,
what do u mean by 2/3 soleniod valves?
Sitrans LR460 Radar level transmitter getting level out or disturbed level during moisture present in the material ie coal in the pccb bunker in CHP.Any suggestions for this problem...????
Definition of reverse and acting controllers:
IN JB CONSTRUCTION WHY WE ARE USING JUMPPER........CAN U PLEASE TELL ME.....
What is the diffrence between digital signal processing and discrete signal processing?
what is the input of digital RPM indicator during the calibration time?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)