In the UVR(Under Voltage Relay) there is a knob for the
hysteresis setting. what is this setting? its threshold is
given from 5% to 50%. please help me....
Answers were Sorted based on User's Feedback
The hystersis is the difference between the voltage at
which the relay operates at and resets at.
For example the UVR is set to open the contacts at 200
volts and it can be set to close at 211.5 volts (for 230
volt sensing). This would be 5% hystersis setting.
This is to stop the relay switching on and off continuously
when the voltage is around 200 volts.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
It should have given in the manual supplied with the
relay.It seems that it is the setting for % drop in
voltage.It is important to set the time delay also.The delay
should not be less than the time taken by any CB of the
power supply system, to clear the fault to prevent tripping
on under voltage due to temporary fault anywhere in the
supply network
| Is This Answer Correct ? | 0 Yes | 2 No |
Please tell me ceilingfan sweep means. Commenly we used sweep1200mm and 600mm MMENLY WE USED CEILINGFAN SWEEP1200MM AND SWEEP600MM
Is there is any hazard to insulation of 3hp motor 5 KV megger is used for it?
why electric shock due to dc is dangerous than that of ac
what is advertised hop count
why the blede and jow of isoletor demage in substation?explan.
what is the healthy specific gravity of lead acid battery used in DG sets ?
3 Answers Bhushan Power Steel,
how we design a pannel to start 10HP motor with the help of star delta starter?
How much of the total hydro power potential has been exploited so far in india?
What is DC power factor??
When One Phase PT Missing (voltage drop ) this time current is zero of This phase(PT Missing Phase) and current is Not Zero of other Phase but PF is always Low That Why
A double circuit with dog conductor 66KV Transmission line from wind farm evacuation to feeding substation having capacity of 25MW for transmission. Can same transmission network be considered for further expansion of Power & how much in MW. If we need to expand next 10-15 MW more will there any augmentation is required in transmission network? Kindly reply asap.
How to Calculate the maximum Demand required for a connected load for a manufacturing Plant
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)