In the UVR(Under Voltage Relay) there is a knob for the
hysteresis setting. what is this setting? its threshold is
given from 5% to 50%. please help me....
Answers were Sorted based on User's Feedback
The hystersis is the difference between the voltage at
which the relay operates at and resets at.
For example the UVR is set to open the contacts at 200
volts and it can be set to close at 211.5 volts (for 230
volt sensing). This would be 5% hystersis setting.
This is to stop the relay switching on and off continuously
when the voltage is around 200 volts.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
It should have given in the manual supplied with the
relay.It seems that it is the setting for % drop in
voltage.It is important to set the time delay also.The delay
should not be less than the time taken by any CB of the
power supply system, to clear the fault to prevent tripping
on under voltage due to temporary fault anywhere in the
supply network
Is This Answer Correct ? | 0 Yes | 2 No |
i need project topics along with circuit diagram in the electrical and electronics engg and also some websites regarding projets.
What is the Ohms low calculation
what are all the components required to assemble solar panel other than pv cell?
What is potientometer.How it is useful in a sychronoscope.
What test must you do before powering up a circuit that you have been working on?
how calculate gd2 of ht motors
4 Answers Hindustan Copper Limited, Kohler India,
Why dnt we generate 5-ph or 7-ph supply like as 3-ph supply
how to work current transformer and potential transformer
Why the transformers are rated in KVA ? in new view
How to size fuse? How to size MCB?
Explain how you intend to work under pressure to meet up with deadline target?
What is the difference between Welding Transformer and Normal Transformer?.