In the UVR(Under Voltage Relay) there is a knob for the
hysteresis setting. what is this setting? its threshold is
given from 5% to 50%. please help me....
Answers were Sorted based on User's Feedback
The hystersis is the difference between the voltage at
which the relay operates at and resets at.
For example the UVR is set to open the contacts at 200
volts and it can be set to close at 211.5 volts (for 230
volt sensing). This would be 5% hystersis setting.
This is to stop the relay switching on and off continuously
when the voltage is around 200 volts.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
It should have given in the manual supplied with the
relay.It seems that it is the setting for % drop in
voltage.It is important to set the time delay also.The delay
should not be less than the time taken by any CB of the
power supply system, to clear the fault to prevent tripping
on under voltage due to temporary fault anywhere in the
supply network
| Is This Answer Correct ? | 0 Yes | 2 No |
what is electricity.
can you please send me the technical questions and aptitude questions of honeywell and jindal steel electrical engg. question paper my e-mail ID is(kkesavanraj@gmail.com)
How will u calculate wire size according to current rating?
what is tha between elcb & rccb?
63MVA,220KV/6.9KV Transformer LV side neutral is connected to Earth pit through NGR. Whether this earth pit required to connect with near by below grouding earth mat or it is to be kept separate?
How to calculate VCB rating for 33KV ,25 MW Power line?
What is the safety factor is to be consider while selecting the switchgear and protection for electrical system
What will be advantage if we put some load in neutral of grounded star transformer & loadshortcircuit current,rated current of cable & MCB with example?
what are upstream faults and downstream faults in power system
Why we use modulus with voltage in stability equation that is P=[E][V]SIN@/X WHY VOLTAGE IS IN MODE VALUE WHAT IS THE REASON?
can any tell me how to do wiring connection in L&T 3ph 4wire E301 CT operated energy meter, what is P1,P2,P3,P0. M1,M2,M3, L1,L2,L3.
2 Answers Bhartiya International,
For 300 MW plant what is the distribution voltage
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)