What is maximum permissible length of cable from transformer
(33kV/0.433kV) HT side to HT panel which contain VCB? In
which standard i shall get this information.
Answers were Sorted based on User's Feedback
Answer / satyajitt_1983
Before calculating the Cable length we have to decided the
cable size which is depend upon the terminal size of
Transformer & HT panel. After selection of cable size & no
of run we have to calculate the voltage drop which should
be within the limit of the specified project.
| Is This Answer Correct ? | 5 Yes | 0 No |
this is a practical problem.
Generally , Station auxiliary or Unit auxiliary
transformers are located very near to load consummer PCC/mcc
building.
High voltage current is less and Low voltage current is
very high,say 1250kva-33/0.42kv,21/1800A,
5MVA,33/0.42KV,87A/7210A. therefore, the distance between
33kv MV SW.GR FEEDER to your transformer location could be
500-1000m as per voltage drop calculation.we have the
system around this distance.
the advatage is LOw voltage from power transformer to PCC
SW.GR IS BUS DUCT. Huge low voltage power cable are totally
eliminated. Maintenanve free. electrical engineering hand
book.siemens ,abb
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pravin
if a long cable is connected what will happen to charging
current & surges that may affect transformer winding. Also
the protection given to transformer is overcurrent & earth
fault that may not work properly, it may mal operate. I am
surching for any standrad that could specificaly mention
this matter.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / pravin
Actualy this problem is occuring in solar power plant. we
need some standard no to justify.
| Is This Answer Correct ? | 1 Yes | 1 No |
That would be subject to your local electrical code. If the
run of cable is outside, usually no limit. Inside there is
a limit to the length. There are provisions if it is
underground such as depth ,conduit type, concrete encased,
maybe others per your code.
Respond to this post.
| Is This Answer Correct ? | 2 Yes | 3 No |
can transformer of different kvas be paralled
How will you explain transformer action in case of 3-phase induction motor?
Why we are putting off the APFC(automatic power factor control) panel while the generator is running?
what is automatic voltage regulator?we can control the vlotage by using fuzzy controller in matlab?why we go for fuzzy?
what is different between IP55,IP54 and IP66?
2 Answers ABB, Global Industries,
is it possible to turn on the single phase star delta on delay timer using 24 v dc ?
Transmission lines usually use a.3 phase b.2 phase c. Single phase
A resistor,inductor and capacitor are connected in series respectively.Voltage across resistor is 40v,across inductor is 70v,across capacitor is 100v.Then what is the total voltage applied across the elements?
WHAT IS THE USE OF PIG TAIL IN WINDOW TYPE CT ?
how to caculate no load loss, load losses & impedance percentage in power or distribution transformers
what is TRCC
according to faraday's law whether the induced emf is average or rms value?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)