Answer / satyajitt_1983
Before calculating the Cable length we have to decided the
cable size which is depend upon the terminal size of
Transformer & HT panel. After selection of cable size & no
of run we have to calculate the voltage drop which should
be within the limit of the specified project.
| Is This Answer Correct ? | 5 Yes | 0 No |
this is a practical problem.
Generally , Station auxiliary or Unit auxiliary
transformers are located very near to load consummer PCC/mcc
building.
High voltage current is less and Low voltage current is
very high,say 1250kva-33/0.42kv,21/1800A,
5MVA,33/0.42KV,87A/7210A. therefore, the distance between
33kv MV SW.GR FEEDER to your transformer location could be
500-1000m as per voltage drop calculation.we have the
system around this distance.
the advatage is LOw voltage from power transformer to PCC
SW.GR IS BUS DUCT. Huge low voltage power cable are totally
eliminated. Maintenanve free. electrical engineering hand
book.siemens ,abb
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pravin
if a long cable is connected what will happen to charging
current & surges that may affect transformer winding. Also
the protection given to transformer is overcurrent & earth
fault that may not work properly, it may mal operate. I am
surching for any standrad that could specificaly mention
this matter.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / pravin
Actualy this problem is occuring in solar power plant. we
need some standard no to justify.
| Is This Answer Correct ? | 1 Yes | 1 No |
That would be subject to your local electrical code. If the
run of cable is outside, usually no limit. Inside there is
a limit to the length. There are provisions if it is
underground such as depth ,conduit type, concrete encased,
maybe others per your code.
Respond to this post.
| Is This Answer Correct ? | 2 Yes | 3 No |
what heppend if we are connected u1-v1-w1 as a star point in the place of u2-v2-w2 in power genration
how the direction of rotation in a dc shunt motor could be reversed?
how we can calcultae the short circuit level for bus bar
0 Answers Jaiprakash, Panorama Apparels,
AC 230V BULB GIVING DC SUPPLY WHAT HAPPENS?
is it possible to turn on the single phase star delta on delay timer using 24 v dc ?
IN SOME CASE, WHEN I GIVE 24VOLTS DC AS INPUT, WHILE IN OUTPUT (THAT MEANS TERMINAL SIDE OF THE INSRUMENTS) I,M RECEIVING ONLY 6 VOLTS, WHAT IS THE REASON FOR THAT MUCH VOLTAGE DROP?
using n1*n2 which type transformer is made; where n1 is primary turn and n2 is secondery turn
what is the multi strand cable size? 0.45mm is area of one strand & 370nos of strand.
How to solve the problem of low voltage at consumer end in distribution system if one phase come low voltage of transformer
what is the highest transmission voltage in india???
49 Answers Bhel, EIPL, Engineering, Jindal,
How does a digital electronic meter work??????
how to calculate the cable size for LT and HT power cables with detail explanation?
2 Answers Asset Developments, Bhel,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)