Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is maximum permissible length of cable from transformer
(33kV/0.433kV) HT side to HT panel which contain VCB? In
which standard i shall get this information.

Answers were Sorted based on User's Feedback



What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel whi..

Answer / satyajitt_1983

Before calculating the Cable length we have to decided the
cable size which is depend upon the terminal size of
Transformer & HT panel. After selection of cable size & no
of run we have to calculate the voltage drop which should
be within the limit of the specified project.

Is This Answer Correct ?    5 Yes 0 No

What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel whi..

Answer / a.p.nanjappa

this is a practical problem.
Generally , Station auxiliary or Unit auxiliary
transformers are located very near to load consummer PCC/mcc
building.
High voltage current is less and Low voltage current is
very high,say 1250kva-33/0.42kv,21/1800A,
5MVA,33/0.42KV,87A/7210A. therefore, the distance between
33kv MV SW.GR FEEDER to your transformer location could be
500-1000m as per voltage drop calculation.we have the
system around this distance.
the advatage is LOw voltage from power transformer to PCC
SW.GR IS BUS DUCT. Huge low voltage power cable are totally
eliminated. Maintenanve free. electrical engineering hand
book.siemens ,abb

Is This Answer Correct ?    3 Yes 0 No

What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel whi..

Answer / pravin0021

Electrical Enginnering

Is This Answer Correct ?    3 Yes 2 No

What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel whi..

Answer / pravin

if a long cable is connected what will happen to charging
current & surges that may affect transformer winding. Also
the protection given to transformer is overcurrent & earth
fault that may not work properly, it may mal operate. I am
surching for any standrad that could specificaly mention
this matter.

Is This Answer Correct ?    2 Yes 1 No

What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel whi..

Answer / pravin

Actualy this problem is occuring in solar power plant. we
need some standard no to justify.

Is This Answer Correct ?    1 Yes 1 No

What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel whi..

Answer / wareagle

That would be subject to your local electrical code. If the
run of cable is outside, usually no limit. Inside there is
a limit to the length. There are provisions if it is
underground such as depth ,conduit type, concrete encased,
maybe others per your code.
Respond to this post.

Is This Answer Correct ?    2 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

Difference between low impedance and high impedance Restricted Earth Fault

0 Answers  


ITI r/tv trade APPLY (J.T.O VACANCEY) ALSO INCLUD AITT ELECTRONIC,WRITEEN XAM DONE 23.03.10 BUT NO RESPONCE WHY ANATHER ID gopal_gh007@rediffmail.com

0 Answers   KBC, wbsedcl,


If genrator not build up voltage , How u can Manually Excite ?

2 Answers  


TRANAFORMER RATING 500 KVA,33KV/433, SECONDARY SIDE SWITCHED ON ONLY CAPACITOR LOAD 140 AMS, PRIMARY SIDE HOW MUCH VOLTS INCREASE?

1 Answers   BPL,


Compare salient pole and cylindrical rotor machines.

0 Answers  


After doubling voltage from solar cells & use step down voltage transformer can we get high current output with low voltage.

0 Answers   Transco,


There is no such thing as a Generator. All power generating devices are Alternator since both generate alternating current since this is the only way electrical power can be generated. In "generators" the alternating current is converted into DC inside the housing of the "generator" in order to give out DC Do you agree? If not please educate me. How else is DC generated if not like above?

2 Answers  


My system is 22kv/3.3kv transformer. client is asking to use NGR, but as we have dedicated Neutral Earthing systems which has a value less than 1 Ohm. So i want solid comparision. Why i should not use NGR as my system is already protected.Can any one help me to get out of this.how should i reply on basis of some great comparision and calculations. Please help

2 Answers   Ariel,


wat are the transmission losses.... how can it be compensated....... wat s power system.......

1 Answers   NPC, NTPC, TCS,


How to increase the backup of three phase ups?

1 Answers  


how to find transformation ratio of squirrel cage induction motor

0 Answers   BITM, WER,


why make protection 85% of winding?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)