Answer / shaik
First of all the voltage ratings given in the question might
be wrong. But the basic rule for calc. the ampacity is to
first find out the current..
Power/ Volts = Amp.
Then the ampacity of the conductor is choosen by taking 125%
of the current.
Here if i consider voltage of this tranformer to be 22/.433
kv. then on primary side the busbar capacity has to be,
1000x1000/22x1000 =45.45 A
45.45x 1.25=56.81 Amps.
Therefore the busbar capacity on primary side should not be
less than 60 Amps.
Similarly, secondary side is calc.
| Is This Answer Correct ? | 5 Yes | 4 No |
THE lv BUS IS DESIGNED FOE 25% OVERLOAD. 1.25 X In. Select
the nearest value as per standards manufacturer,.If you
exact your figures, supplier quote high price.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the drawback of static coefficients?
electricity board have asked me what size meter i need fitted in my garage, its a 415volt supply and i want to run six 20amp supplies tolifts and things plus ten florry lights , what kva meter do i need??
Define cut-off rate?
i have 2kv ups how many watts batteries is required
Why the colour of insulator is always is chocolate in colour?
In case of 3Phase Supply, Voltage R-Earth/Neutral - 220 Y-Earth/Neutral - 220 Z-Earth/Neutral - 220 Total is -> 660Volts Then Why it is said that 3Phase supply is 440
6 Answers Hindustan Unilever Limited,
Is it possible to connect a safety device in to parallel?
i want to know d working mechanism of tafe tractors next i like to know d engine type of apache bighs can anyone help me
If I have a LT panel 3ph, 415V, 50Hz which demand load-600kw, how we can calculate its body earth strip size.
what is the disadvantages of common earthing for AC and DC equipment? (i am talking about inverter control room and inverter duty transformer earthing is common...?)
11 kv metering is done in my factory.Meter show PF 1.000 but kvarh lag&lead show 24&94 respectively & Avg.PF is .956 .? is what i do for inproove my PF to 1.000
WHAT IS THE COMPLETE DEFINATION OF POWER FACTOR?HOW IT CAN BE IMPROVED?AND WHAT IS CAPACITIVE LOD AND INDUCTIVE LOADS
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)