how to calculate busbar capacity for 1000Kva transformer having22/.433V
Answers were Sorted based on User's Feedback
Answer / shaik
First of all the voltage ratings given in the question might
be wrong. But the basic rule for calc. the ampacity is to
first find out the current..
Power/ Volts = Amp.
Then the ampacity of the conductor is choosen by taking 125%
of the current.
Here if i consider voltage of this tranformer to be 22/.433
kv. then on primary side the busbar capacity has to be,
1000x1000/22x1000 =45.45 A
45.45x 1.25=56.81 Amps.
Therefore the busbar capacity on primary side should not be
less than 60 Amps.
Similarly, secondary side is calc.
Is This Answer Correct ? | 5 Yes | 4 No |
THE lv BUS IS DESIGNED FOE 25% OVERLOAD. 1.25 X In. Select
the nearest value as per standards manufacturer,.If you
exact your figures, supplier quote high price.
Is This Answer Correct ? | 0 Yes | 0 No |
What are your personal skills and abilities for such a Master Course and your possible preparation to undertake this course?
why we generally use 3.5 core cable or in other word 1/2 core for neutral and also confirm me that in balance conditiob(3 phase)current in neutral will zero
7 Answers HCIL, Jindal, Siemens,
When we use air circuit breaker, it has O/L protection ,time delay SC protection, Instataneous SC protection & ground fault protection. They all have some setting range. But what is the suitable/allowable setting for the above protection which will be safe for the equipment? For example-O/L protection setting have a range of (0.4,0.45,0.5,0.55,0.6,0.65,0.7,0.8,0.9,1.0)xIn Time delay SC protection have a range of (1.25,1.5,2,3,4,6,8,10,12)xIn Time delay setting is 0.02,0.1,0.2,0.3,0.4 Instataneous setting is fixed to 20xIn Gound fault setting is given 100A,300A,600A,900A,1200A This setting are for 2500A ACB. So what will be the basic allowable setting for the above protection? is there any formulae to calculate this<
I want to design a heating coil of 80/20 nicrome for 3.5KW please give me the calculations choosing for physical dimensions assume coil voltage will be 110V AC assume necessary conditions
If the battery is in charging condition means, battery is which type of load? Capacitive or Resistive load?
What is the role of feedback in a closed loop control system?
what is meant by bus bar and outgoing/incoming breaker in an electrical/electronic circuit
What is Synchronization of generator,where and how it is achieved.
. Is there a simple method to measure the horsepower of a small motor (1-3 hp) for a non-technical person
1 sq mm conductor=? how many amps
What is the diference between increased saety motors and non sparking motors?
When we have earthing mesh or underground earthing network in industrial plants, weather we have NT-S or NT-C-S kind of earthing system, so eventually weather we must use 4 or 5 wire in 400 volt level (For example 3×150+70 mm2 or 5×150 mm2) in this connection I would like to know exactly the paragraph of IEC or IEEE number