which fault current is maximum: 3 phase short circuit, LG,
LL or LLG?? why??
in one of the problems that i have solved, 3 phase short
circuit current on an unloaded generator came out to be
less than the LG fault current. can anybody please explain
why.
Answers were Sorted based on User's Feedback
Answer / shubham gupta
it depends upon the grounding method employed.
LG fault current is more if the generator is solidly grounded.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / dr rajan
It is always the 3 phase bolted fault. Check your problem
again. You may have made a mistake. Why 3Ph fault current is
high?
When all phases are grounded or shorted, the impedance is just
let us say X in each phase leading to V/X x 3 times. where as
when you have LG, you will include the line impedance in
series with X, equals X+xL, which is more than X on 3Ph short
ckt. When you divide V/(X+xL) what will you have???? More
current or less current???????
Is This Answer Correct ? | 1 Yes | 2 No |
what is model question rrb junior engineer electrical gr.II
How to calculate the current in DG What are the type of power pls explain with related formulas
1 Answers Corona Enterprises, Sodexo,
1 no. 22 kV feeder is taken from state electricity board. 350 MVA is the S.C. MVA. now i am feeding this feeder to HT Panel having 2 outgoings which further supply to 2 Transformers. Can you please suggest me the type & rating of cables are 3 of these cables same? or they are different? please help...............
What happens if the secondary of the transformer is shorted?
Which type of moter is used in trains, what is the ratting of supply used explain Working principal?
What is the breaking capacity of transformer and how can we calculate the breaking capacity of tranformer
Can anybody tell me how to calculate(formula) earth flat size(for copper and aluminium).
How the neutral earthing is connected in DG alternator
i want to know about psu exam eligibility critaria?
why generation is done in delta nad transmission in star? brief
Why the frequency of a system is changed if the load changes?
what is max. continous current of LT side of distribtion transformers? ie for25kVA, 63kVA, 100kVA, 200kVA etc