what will happen if we double the input frequency of a
transformer keeping the voltage constant?
Answers were Sorted based on User's Feedback
Answer / santhosh
hysterisis losses and eddy current losses depends upon v/f
ratio hysteris loss=kB^1.6 f v if v/f ratio is constant
hysterisis loss is prportional to frequency i.e B is
constant if v/f is not constant hyloss is prop to f^-0.6 so
if freq is is increased hyloss is reduced but eddy current
loss remain constant because eddyis prop to B^2 f^2 so if we
sub v/f in the place of B eddy loss is prop to V^2 so it is
indepentent of frequency
| Is This Answer Correct ? | 38 Yes | 1 No |
If the frequency applied to a transformer is increased, the
inductive reactance of the windings is increased, causing a
greater ac voltage drop across the windings and a lesser
voltage drop across the load. However, an increase in the
frequency applied to a transformer should not damage .
But, the applied frequency of the transformer is less than
the normal Frequency, the reactance of the windings is
decreased and the current through the transformer winding is
increased. If the decreasing frequency is enough, the
resulting increasing current will damage the transformer.
For this reason a transformer may be used at frequencies
above its normal operating frequency, but not below that
frequency.
| Is This Answer Correct ? | 18 Yes | 4 No |
Answer / dinesh b.e
The same current will flow for both 50 and 100Hz frequency.The Only difference is hysteresis losses will be more if 100Hz given as input. .Which only used to test the transformer's for 60second to check insulation withstand capability. .Generally hysteresis losses will be there in transformers which depends upon core quality. .Magnetising and Demagnetizing of core for 100cycles leads to increase in hysteresis loss.That is losses in form of heat .Which gives raise to increase the oil temperature.Due to this effect , chemical reaction Will take place between copper and sulfur content in oil.finally formation of copper sulphate,which acts as a conductor and settled upon windings . circulating current Will be there due to mmf.which leads to heat and damages the windings dielectric strength.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shinde kv
when we applied double freq. that time eddy current losses
increase means iron losses will be increase hence increase
the heat loss.
| Is This Answer Correct ? | 8 Yes | 14 No |
Answer / daxity
Current is the RATE of flow of CHARGE in a circuit.
Frequency is the number of CYCLES per second......NOW..if
frequency is increased,the rate of flow of charge is
increased that is current,which may damage the insullation
on transformer winding due to over heating.
| Is This Answer Correct ? | 1 Yes | 8 No |
In all the generators, the excitation supply is DC. What is the significance of DC excitation? What will happen if AC supply is given as excitation supply?
why control circuit voltage always chooses to be 110v and 220v? and in where it is 110v and 220v? and in where it AC and DC?
how to get more than 1000 ohms between 2 earth pits ?
is it possible for different brand of H.V transformers to run or operate in parallel to each other? if so how much disturbance can this affact the H.V bus bar?
A power transformer 4MVA/11KV/0.415Kv has been out of use in 12years. what maintenance actions/test need to be carried out before energizing.
I want to know Electrical Circuit?
Define CT & its function
This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/11kV three phase star - star power transformer. The neutral was solidly connected to the earthing mat. But because of high resistance of earthing mat (130 ohm on LV and 180 ohm on HV), one day LV side neutral earthing conductor melted and we had a huge damage. Can any one plz tell me what might happen when we connect power transformer neutral to the earthing mat which has high resistance (>100 ohm ) ?????
What is meant by reset level of the relay?
HOW CAN YOU CALCULATE PRACTICAL EFFICIENCY OF A ASYNCHRONOUS INDUCTIONMOTOR OF 7.5KW,& MOTOR IS RUNNING WITH AVOLTAGE OF 410 VOLTS,& TAKING CURENT OF 13 AMPS
what are the protecyion of transformer & generators
what is the response time of relays when a FAULT OCCURS IN A POWER SYSTEM?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)