How you take care of a motor from over loading and what are
the different overloading ratings of different motors?
Answers were Sorted based on User's Feedback
Answer / daher
use overload circuit breaker to protect it, thermal
overload protects your motor againts overloading or/and
overthermal switch mount it on the motor stator.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / aditya sharma
Overload relay will be use for overload protection
Different different rating of overload relay
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nikhan
# 1 Motor
Rating Motor F.L.C in Amp
0.25 KW 0.4725
0.37 0.6475
0.5 0.9625
0.75 1.3125
1.1 1.925
1.5 2.625
2.2 3.85
3 5.25
3.7 6.475
4 7
5 - 5.5 9.625
7.5 13.125
9.3 16.275
11 19.25
15 26.25
18.5 32.375
22 38.5
30 52.5
37 64.75
45 78.75
55 96.25
75 131.25
90 157.5
110 192.5
132 231
150 262.5
160 280
200 350
250 437
| Is This Answer Correct ? | 0 Yes | 2 No |
Motor
Rating Motor F.L.C in Amp
0.25 KW 0.4725
0.37 0.6475
0.5 0.9625
0.75 1.3125
1.1 1.925
1.5 2.625
2.2 3.85
3 5.25
3.7 6.475
4 7
5 - 5.5 9.625
7.5 13.125
9.3 16.275
11 19.25
15 26.25
18.5 32.375
22 38.5
30 52.5
37 64.75
45 78.75
55 96.25
75 131.25
90 157.5
110 192.5
132 231
150 262.5
160 280
200 350
250 437.5
| Is This Answer Correct ? | 1 Yes | 5 No |
at work we have a 3 phase motor but on testing one phase isnt getting a reading. it runs 24 hours a day all week. stops and starts well no noise or heating. the phase isnt down to earth.is it just a bad meter reading or not? phases one and three came up with a resistance reading of 0.4 but phase 2 couldnt get anything shows up as open circuit.
what is magnetizing and demagnetizing current in generator and motor?
What are the advantages and disadvantages of oil filled transformers?
2 Answers Mercantile Marine Department, Studio College,
what is the difference between rectifier and converter and commudator?
what is doid
What is a variable speed motor?
why any Elelctricity board insist not to change the buren of their metering CTs or PTs for metering purpose? as a example elect. board not accepted that any customer change their metering CT or PT core burden from 5VA to 15VA.. why?
What are the different protection systems takes place on control panel board?
how to find the torque of the single phase synchronous motor by doing an experiment
the site measured knee point voltage of protection class CTs should be greater than rated knee point voltage? what about meetering class CTs. Should it be below the rated knee point voltage?
i have been tasked with a design of protection, metering and control(PMC) relay panel extension to accommodate all PMC relays.There is an already existing panel where this one will be built.What are the design aspects for this kind of project? thank you.
earth also having a gravitational force (magnetic field of north and south)but it attracts any object compare to this theartifical magnetic cant perform same as earth why?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)