Answer / mahesh babu-calicut
kva is the actual power delivered from transformers and
generators.kw is the active power consumed by loads.KVA IS
THE VECTOR SUM OF KW AND KVAR
| Is This Answer Correct ? | 31 Yes | 0 No |
Answer / prakashchandra rana
kw= root 3*v*i*pf
kva= root 3*v*i
so the differnce between kw and kva is pf.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / p.gupta.1852
kVA means kilovoltampear. It is a power of transformer
having zeero power factor whereas kw is stands for kilowatt
and it a power of load having power factor whether legging
or leading.
| Is This Answer Correct ? | 11 Yes | 12 No |
Answer / dhaval
kva is the actual power delivered from any equipment and
kw is unit of power.
kva = kilovoltampear
kw = kilo watt
| Is This Answer Correct ? | 1 Yes | 5 No |
Safety measures in air circuit breaker
5 Answers Megatron Solutions, TCS,
it is used to measure the potial difference between two point?
why supervision relay is used in incoming feeders?
design a LV scheme for a 15 storied building?
difference between earthing and grounding?
If Ac supply is given to the DC motor then what will happen? clear explanation
What is stepper motor?
If I have a LT panel 3ph, 415V, 50Hz which demand load-600kw, how we can calculate its body earth strip size.
in case of OC+EF relay, how the burden is divided/calculated/shared by the CTs in case of normal (healthy condition) and during fault conditions.? three coils of OC & ef coil is conected in residual connection across the three CTS.
what are different types of electrical windings? i know the distributed winding ,concentrated winding etc but i want some detailed information, in what condition we will use distributed,concentrated windings what are the difference between them which is best, how induced emf changes by using different types of windings 20 hours ago - 1 week left to answer
we can stepdown the voltage from 230/12v ,and we use the voltage for various electronics components why can't we step up the voltage from 12/230v if we can shall we use the voltage for domestic single phase supply
Why there is no provision of breaker in between primary of UAT and generator
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)