Is 3 phase induction motor can work as a generator?? if so
why & how??
Answers were Sorted based on User's Feedback
Answer / kotaprolu.raneela
if the speed of the rotor is made more than synchronous
speed then slip becomes negative as a result it behaves
like induction generator
| Is This Answer Correct ? | 29 Yes | 0 No |
in other word, if the motor loss of synchro with the supply
| Is This Answer Correct ? | 0 Yes | 0 No |
Hi friends. is it possible that SCADA System through RTUs can connect Via PLCC Communication carriers ? thanks
why transformer ratings in kva? & DG ratings in kva? & Motor ratings in kw/HP?
When we change the tap position of 10MVA transformer it suddenly tripped with Out of step indication and also with Static differential relay indication, Transformer Bucholz relay indn and Low oil level indication. Before 1 week the same problem occured by changing the tap position. but at that time only oltc bucholz relay activated. After testing the TxR Relay team & PET team cant find any solid reason. The values are ok also. So plz answer wat's the reason for this incident? anybody plz help.
Dear Friends, I have a 500KVA transformer supplying whole factory having 3 phase and single phase mixed loads. Power room has ammeters connected via CTs for individual phase. Now I know that readings shown on meter for each phase say R,Y and B are line currents. But when I want to know the total on transformer do I need to add the currents of all three phases readings shown on meter or value for anyone phase will give me the correct power load on transformer for that point of time. 2. If ammeter shows unbalanced readings for R,Y, B phases say 150, 250 and 300 respectively so can I assume that 150A i.e average of 3 will be the 3phase load currents and remaining will be 1phase currents. Please clarify my doubt.
what the is the distance between 110kv termination point and the ground. how to calculate
How to calculate Battery back up time for a 400 AH Battery bank having a load of 20 Amps and charging time required to fully charge this battery bank?
Why not implimenting power factor in Diesel generator
as we see that in our country the power rating for transmission is always rated in multiple of 11 like 11kv,33kv,66kv132kv. So i want to know wht is reason or logic here.
How much area is covered by a single lightning arrestor to protect object from lightning strokes ?
how can get electrical "c" licence.i am complited in DEEE.PASSING YEAR OF 2010 I AM WORKING IN SPENCER PLAZA ELECTRICAL MAINTENANCE ,I AM DIPLOMA COMPLEATED IN ANDHRA PRADESH AND WORKING OF TN PLEASE HELP ME
What are the three major categories of error?
sir i applied for hpcl(electrical).i want to know from which subjects most of the technical que will b asked.and pattern of the written test.pls help me
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)