Is it necessary to carry out sheath test after cable
jointing? If the value is zero of such instance , is it ok
to energize the cable?
Answer / k.prakashchandra
If you get zero ohm on sheath test ,sheath continuity is
confirmed.You can energize the cable after testing insulation
| Is This Answer Correct ? | 1 Yes | 0 No |
. What should be the minimum and maximum ohmic value for earthing?
why the power factor in inductive load is lagging while it is leading in capacitive load?
1) Can anyone give me a typical value for Insulation Resistance of 11kV xlpe cable? 2) How much will the IR value decrease per KM of cable length added?
why CRGO material used in transformer?
how many desk top computer can connect to a 25kva 3phase generator?
Why are iron cores in transformers made laminated?
Slow acting fuses are most often used for which application a) Lighting circuit b) heating circuit c) Motor D) Radar circuit
What is the difference between grounding & earthing?
What is the difference between induction motor and the Synchronized one?
What is the effect of positive feedback on the stability of the systems?
where does the unbalanced current flow in the delta circuit
advantage of motor design on higher power factor . normally motors are designed for .8 power factor. what is advantage of designing at .88 power factor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)