Answer / atif rasheed khan
there are two cases arises here, in first case our answer
will be yes under the following condition.
the generator should be so excited till its voltages
produced be equal to the previous step up voltages done
through transformer, however these rise in voltages are just
restricted to 33KV, because beyond this voltage level there
arises a critical issue of the winding insulation.
in this method just reverse the connections, i-e change the
L.T as sending voltage side, and the H.T as generation side.
however in the second case , our answer will be no, if
higher voltage step up transformer are used, due to the
above mentioned problem of insulation of transformer.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
We have to back-charge UGT if the synch is done at generator
output and may be for aux supply
| Is This Answer Correct ? | 0 Yes | 0 No |
Yes. If the aux tr is connected to GT and there is no generation ,the GT is back charged with grid duly isolating gen, for aux supply .
| Is This Answer Correct ? | 0 Yes | 0 No |
Our Company's Contract Demand is 110 kVA. We use 12 Capacitors each of 12.5 kVAr Capacity to maintain Power Factor of 0.99. So, what steps should we take so that our Contract demand does not exceed 110 kVA?
Can anybody tell me how to calculate(formula) earth flat size(for copper and aluminium).
what is the use nuetral wire
what is the difference between normal motor and flame proof motor??
role of europe union in UK safety legistlation (electrical safety)
WHAT IS TANK CKT.?
Why the substation measure in KV but not in the power ratings of transformer.
CTs Ratio
In which of the following case, the rotating magnetic field is reversed? A regenerative breaking B plugging C dynamic breaking D forward motoring
any calculation method for decide cable size for current?
sir what is the minimum IR value of 11 KV alternator?
I have a table fan of Rallifan Make. When I overhauled it I found a stator winding and an aluminum die cast rotor. So it is supposed that it is a 1 phase induction motor. But there are only two terminals coming out and there is no capacitor. Can any one tell how this motor works? or which type of this motor is?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)