why ct output is in 5A?
Answers were Sorted based on User's Feedback
Answer / sudhakar g
Beacuse the ct output can use for relays, load managers or
any other devices which can consume low
current.........they also mention the burden and class like
15VA and CL 1.0....
Is This Answer Correct ? | 13 Yes | 0 No |
Answer / alan jenkins
Traditionally protection CT's were 5A output and a high vA because they had to drive electro mechanical protection relays which had a high burden, However with modern Digital and Numerical Protection relays the operating burden is very small hence the CT's dont have to be as big as they used to be. Also on modern distribution networks, fault currents can be very high and 5A CT secondary currents were also equally high.
much favoured on new and refurbished equipment is 1A CT's.
Is This Answer Correct ? | 0 Yes | 0 No |
R=*¶ l/a
Explain difference between aluminium coductor & copper coductor.
how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details three phase motor 75 kw,415 v,.85 pf,50 hz?
how to calculate kvar in Akiva
In EB metering we face problem kva jump even in no load condition.can any one help to control this
where the lexical paramater will use in fron end?
When calculating the speed of a rotor required for a particular frequency of synchronous generator we use the equation 60f/p Is this p is the number of pole pairs of rotor & do we consider the number of pole pairs in the stator is 1?
Match the following a)(X'+Y') b)X'Y' C)XY 1)NAND 2)NOR 3)Carry
control wiring purpose,standards, ferrule code standard, interlock, schematic, symbol
How they LT panel busbar size choose
what is a pilot wiring and whys that called a pilot wiers
why motor range is available 22kv,30kv,37kv,45kv and so on? why motor range is not available 21kv,24,25,26,27kv and so on?