What is the function of trip neutral close switch?

Answers were Sorted based on User's Feedback



What is the function of trip neutral close switch?..

Answer / ravi kumar

TNC switch is nothing but two position switch. when it is
in close position it will put the circuit breaker in
operation by energising the closing coil and when it is in
trip position it will trip the circuit by energise the trip
coil in circuit breaker.

Is This Answer Correct ?    77 Yes 15 No

What is the function of trip neutral close switch?..

Answer / minimanu

IT is a three position Switch. The swith atre of two types -
Having lockable Trip position and other with spring return
to normal Neutral position.
For manual operation this switch is used to TRIP a breaker
by moving it towards trip position and close by moving it
towards Close position.

In neutral position all the operations on AUTO mode or from
remote can be done, as per the scheme.

For keeping the breaker in OFF condition or for isolation,
the switch can be kept in lockable TRIP position, if that
facility is available in the switch.

Is This Answer Correct ?    52 Yes 6 No

What is the function of trip neutral close switch?..

Answer / vikas s adhatrao

TNC switch is a three position switch, used for closing or
tripping a circuit breaker manually from panel (locally).
this switch is spring loaded, this ensures that switch
returns to neutral position after any operation (either
close or trip). This is required to isloate the closing /
trip coils, which are short time rated, from the control
supply.TNC switch makes close open commands momentary.

Is This Answer Correct ?    23 Yes 5 No

What is the function of trip neutral close switch?..

Answer / pks

trip neutral close is the switch of breaker thro' which we
can keep the breaker energised thro' closed coil, we can
keep the breaker in off condition thro' trip coil or
breaker can be used in operation mode auto by keeping on
neutral..

by using TNC switch manually we can energise the CC or TC
of breaker.

Is This Answer Correct ?    18 Yes 6 No

What is the function of trip neutral close switch?..

Answer / varma

TNC is a 3 position switch used for closing or tripping a
circuit breaker manually from panel locally. TNC siwtch
returns to Neutral position after any operation.

Is This Answer Correct ?    10 Yes 6 No

What is the function of trip neutral close switch?..

Answer / akhilesh solanki

TNC Switch is normally used for the breakers. This is not simple Control switch with spring loaded. The special features of the TNC Switches are as below.
1. Close can be done only after tripping the breaker. This is required to ensure that successive operation of closing coil can not be done.Required for safety of closing coil.
2. It can give status of last operation i.e. Close or trip.
3. As per standard practice Trip will always be on the left side and Close will be on the right side.
4. This can be locked in certain position mostly in Trip Condition so that it can not be operated
5. Some of the above listed features are requirement specific but a normal TNC switch breaker shall have all of the above except Point no. 4.
6. Normal Two / three position switch with spring loaded back to normal shall not be used as TNC Switch

Is This Answer Correct ?    4 Yes 0 No

What is the function of trip neutral close switch?..

Answer / vikas laller

IT is a three position Switch.When it is
in close position it will put the circuit breaker in
operation by energising the closing coil and when it is in
trip position it will trip the circuit by energise the trip
coil in circuit breaker.

Is This Answer Correct ?    3 Yes 0 No

What is the function of trip neutral close switch?..

Answer / sanket patil

A TNC SWITCH IS ALSO CALLED BREAKER CONTROL SWITCH. IT IS
LOCKABLE IN THE NEUTRAL POSITION AND IS A THREE POLE SWITCH.
WHEN IT IS IN CLOSE POSITION THE COMMAND IS GIVEN TO THE
CLOSING COIL OF THE CKT BREAKER AND THE BREAKER CLOSES.
WHEN IT IS IN THE TRIP POS COMMAND IS GIVEN TO THE TRIP
COIL OF THE CKT BREAKER AND THE BREAKER TRIPS.

Is This Answer Correct ?    9 Yes 7 No

What is the function of trip neutral close switch?..

Answer / amit tiwari

It is as simple as TNC (Trip Neutral Close) in normal condition the switch will be in NEUTRAL position. To close the Circuit breaker we have to rotate it in direction 'C' as mentioned in TNC switch and breaker will be in operation and if we want to trip the circuit breaker we have to rotate the switch in the direction of 'T' as mentioned in TNC switch and breaker will get tripped for maintenance. Remember TNC will operate from field. Remote closing and tripping can be done as TNC switch will be in 'N' position.

Is This Answer Correct ?    3 Yes 1 No

What is the function of trip neutral close switch?..

Answer / sunil kumar

TNC switch is a three position switch. when it is
in close position it will put the circuit breaker in
operation by energizing the closing coil and when it is in
trip position it will trip the circuit by energize the trip
coil in circuit breaker. But the switch After energize the coil it is going on in neutral position Automatically.

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

What is meant by soft starter used in motors?

4 Answers  


what are the effects on an power plant and consumers if the power factor is increased or decreased?

2 Answers  


Do we really need wheels for the transformer

1 Answers  


Difference between MCC and PDB

3 Answers   BARC, CDS, NINL,


whate is the meaning of balance/unbalance,in stabilizers type

0 Answers   TCS,






What is the minimum distance between taransformer (say 2000 kva)and its earth pit?

2 Answers   Bhel,


How to choose size of the cable w.r.to current carrying capacity ...

0 Answers   L&T, Saams,


how power can be saved using VFDs in detail explain

1 Answers  


What is the voltage b/w nutral and earth

11 Answers   Mind Space,


I HAVE A INCOMING 100A MCCB TPN 25KA, CABLE LENGHT OF 80M 70MM CABLE SIZE FROM MAIN SUBBOARD TO NEW DB.BASE ON THE FAULT LEVEL SETTING OF 45KA.I WOULD LIKE TO FIND OUT 25KA ENOUGH KA. APPRECIATE IF SOMEBODY CAN ASSIST ME WITH FORMULA FOR THIS. FRM: JEFF

0 Answers  


Why Neutral Isolation is required?

0 Answers  


What is ahu ? Working principal.

0 Answers   Sodexo,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)