I have 725KVA DG set how to Calculate the Ratio of KWH?
Whatb is the Formila
Answers were Sorted based on User's Feedback
IT is very sample . Normaly DG's power factor is about to
0.8 .
We multipli the pf from kva , we get KWH of DG.
KWH= KVA*pf
KWH= 725 * 0.8
= 580 KWH
| Is This Answer Correct ? | 50 Yes | 10 No |
Answer / satish s.nanal
The Term Ratio of KWH itself is incorrect.
KWH means Energy Consumption.It is multiplication of Watts
( Or Kilowatts) consumed over a period of time.Now
considering Power Factor of 0.8 , KW shall be = 725*0.8
= 580 KW.
Now if 580 KW are consumed for say 2 Hours then Energy
Consumption will be 580*2= 1160 KWH
| Is This Answer Correct ? | 30 Yes | 3 No |
Answer / ramali
In any DG sets, power factor should be mentioned.Either it
is 0.7 to 0.8.
so, first we calculate the KW,
KVA*pf=kw
725*0.7=507.5kw
725*0.8=580Kw
now KWH is according to power consumption in your DG.
Hence, your 725KVA DG should gives 580Kw per hour max.
this calculation contains temp,cable laying method,cable
quality,lugs, crimping,fixing bolt nuts etc.,
| Is This Answer Correct ? | 28 Yes | 5 No |
Answer / bala
power=1.73*V*I*p.f kwh
V- Average voltage per hour
I- Average current drawing per hour
P.F- Average power factor per hour
| Is This Answer Correct ? | 23 Yes | 16 No |
Answer / girish chandra adhikari
The term of KWh is itself incorrect. Rather we should say
how to calculate the DG. Ratio ?
For calculating DG.ratio we should calculate the total unit
consumption ( Kwh ) and also calculate the total HSD(Fuel)
consumption. Then the DG. ratio would be Total KWh/Total
HSD Consumption in one hrs.
Suppose your 725 KVA DG Unit consumption in one hrs is 400
and HSD.consumption is 110 Lts. DG.ratio = 400/110 =3.63
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / jagjeet
power=1.73*V*I*p.f kwh*efficiency
V- Average voltage per hour
I- Average current drawing per hour
P.F- Average power factor per hour
| Is This Answer Correct ? | 7 Yes | 10 No |
Answer / amit sonmale
Its verry Simle 1stlly I want to know The Current
CApacity Of d.g Set It means I=Kva/P.f
725/0.80
=906.25 Amps.
Then Know Load Capacity Kw =V*1.732*.80*I/1000
=415*1.732*0.80*906.25/1000
=521.1155Kw
| Is This Answer Correct ? | 16 Yes | 22 No |
is the surge effect the solar panel, if yes so tell me how can surge effect the panel? explain brifly
What is the general power consumption rating of CPU CRT type and Flat type, Monitor,Printer, projector, Scanner?
What happens on the secondary of a 33kV/11kV when one phase of the primary fuse blows?
How can we calculate the power factor of an electrical appliance ? Is there any formula ? Is there any meter around to calculate it ? And how to use that meter ? thanks
what about electrical pannel.? What is meant by plc pannel.?
what will happen if the frequency supplied is more than the frequency of the instrument...?
why DC source is used to idetify the polarity of CT/PT?
If ac voltage applied to the field of dc generrator the output of dc generator ?
what are inherent currents?
In Star type and Delta type Motors, If one phase will miss/Break then which phase winding will burn and why?
What's the difference between non break power supply and non break non short break power supply
What is class ab operation?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)