I have 725KVA DG set how to Calculate the Ratio of KWH?
Whatb is the Formila

Answers were Sorted based on User's Feedback



I have 725KVA DG set how to Calculate the Ratio of KWH? Whatb is the Formila..

Answer / prakash veer singh

IT is very sample . Normaly DG's power factor is about to
0.8 .
We multipli the pf from kva , we get KWH of DG.

KWH= KVA*pf
KWH= 725 * 0.8
= 580 KWH

Is This Answer Correct ?    50 Yes 10 No

I have 725KVA DG set how to Calculate the Ratio of KWH? Whatb is the Formila..

Answer / satish s.nanal

The Term Ratio of KWH itself is incorrect.

KWH means Energy Consumption.It is multiplication of Watts
( Or Kilowatts) consumed over a period of time.Now
considering Power Factor of 0.8 , KW shall be = 725*0.8
= 580 KW.
Now if 580 KW are consumed for say 2 Hours then Energy
Consumption will be 580*2= 1160 KWH

Is This Answer Correct ?    30 Yes 3 No

I have 725KVA DG set how to Calculate the Ratio of KWH? Whatb is the Formila..

Answer / ramali

In any DG sets, power factor should be mentioned.Either it
is 0.7 to 0.8.
so, first we calculate the KW,

KVA*pf=kw
725*0.7=507.5kw
725*0.8=580Kw
now KWH is according to power consumption in your DG.
Hence, your 725KVA DG should gives 580Kw per hour max.
this calculation contains temp,cable laying method,cable
quality,lugs, crimping,fixing bolt nuts etc.,

Is This Answer Correct ?    28 Yes 5 No

I have 725KVA DG set how to Calculate the Ratio of KWH? Whatb is the Formila..

Answer / bala

power=1.73*V*I*p.f kwh

V- Average voltage per hour
I- Average current drawing per hour
P.F- Average power factor per hour

Is This Answer Correct ?    23 Yes 16 No

I have 725KVA DG set how to Calculate the Ratio of KWH? Whatb is the Formila..

Answer / girish chandra adhikari

The term of KWh is itself incorrect. Rather we should say
how to calculate the DG. Ratio ?

For calculating DG.ratio we should calculate the total unit
consumption ( Kwh ) and also calculate the total HSD(Fuel)
consumption. Then the DG. ratio would be Total KWh/Total
HSD Consumption in one hrs.

Suppose your 725 KVA DG Unit consumption in one hrs is 400
and HSD.consumption is 110 Lts. DG.ratio = 400/110 =3.63

Is This Answer Correct ?    11 Yes 4 No

I have 725KVA DG set how to Calculate the Ratio of KWH? Whatb is the Formila..

Answer / jagjeet

power=1.73*V*I*p.f kwh*efficiency

V- Average voltage per hour
I- Average current drawing per hour
P.F- Average power factor per hour

Is This Answer Correct ?    7 Yes 10 No

I have 725KVA DG set how to Calculate the Ratio of KWH? Whatb is the Formila..

Answer / amit sonmale

Its verry Simle 1stlly I want to know The Current
CApacity Of d.g Set It means I=Kva/P.f
725/0.80
=906.25 Amps.
Then Know Load Capacity Kw =V*1.732*.80*I/1000
=415*1.732*0.80*906.25/1000
=521.1155Kw

Is This Answer Correct ?    16 Yes 22 No

Post New Answer

More Electrical Engineering Interview Questions

WHAT IS THE MEANING OG (li = 7 In)

1 Answers  


why dc series motor high speed motor

3 Answers  


How to calculate the actual 3phase power, if the load current of each phase is not balanced

2 Answers  


In Ferantti Effect Receiving end voltage is greater than sending end voltage but how it is possible. I know its all about charging current but give me some more detailed explaination?

3 Answers  


If I want to buy a new Xformer for my plant what are the main parameter will I need to check?

1 Answers  


which protection are used for turbo generator in thermal power plant.

1 Answers   Grasim,


how to calulate multiplying factor if meter ratio is /5 ampere and ct ratio is 100/5 ampere.(our supply is 3 phase 415 volts)what is multiply factor?

3 Answers   Vivek Engineers,


transformer cooling fan kharab ho jaye to 1-off kar dena chahiye 2-load kum kar dena chahiye 3-koi frrk nhi padta 4-sub galat hai. choose right option

2 Answers   PGVCL Paschim Gujarat Vij Company Limited,


what is difference between line differential and transformer differential?

1 Answers   L&T,


how many single tension hardware are required on a double circuit transmission tower?

1 Answers  


what is load shedding

4 Answers   KSEB,


xfhnchncv?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)