calculate multiplication factor of a trivector meter with
line ct ratio 200/5A, line PT ratio 11000/110V and meter CT
ratio 200/1A and meter pt Ratio 11000/110V.
Answers were Sorted based on User's Feedback
Answer / shyam sunder thakur
The meter in this case can carry up to 40A current only as meter CT rating is 200/1,
Multiplication Factor if calculated is under
Adopted(line) CT Ratio X Adopted(line) PT Ratio
M.F =--------------------------------------------------
Meter CT Ratio X Meter PT ratio
200/5X11000/110
=----------------------------= 1/5=0.2
200/1X11000/110
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / k.prakashchandra
If the line CT were of 200/1 ratio, the meter would read
correctly. As the ratio is 200/5, for 200 A primary current
the sec current will be 5 A instead of 1.0 .Hence you have
to divide the reading by 5 ,if it is capable of taking 5A.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / ajaz kirmani
Multiplication Factor MF = [ (200/1)x(11000/110)]
-------------------------------
[ (200/5)x(11000/110)]
MF = 5
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / jaskanwar
In a CT PT connection if there is a LTCT meter of 200/5 installed instead of HT meter of -/5 A . Then what will be the MF for this situation.
CT PT = 10/5 A
| Is This Answer Correct ? | 0 Yes | 3 No |
What is a soft start?
what is the dedicated neutral earth in ups? y its required?
how many wires need to be bring to the motor if its star delta starter
What will happen if i replace a inductive proximity switch with photo sensor in a machine?
what is the difference between energy efficient and high efficiency motors
what is the effect of power factor in electrical circuit ? if we mainten power factor near about unity (0.999) our energy consumption Units increase or decrease?
11 Answers Piramal Healthcare,
Transmission through a short line depends on
why transmission is only 3 phase and not 2 or 4 or poly phases
Can a dc motor works as a dc generator. If yes , then how?
Draw an S.L.D of the main panel for a hospital, showing meter position. Essential loads are: 1) Equipment load 100 KW 2) Critical load 500 KW 3) Life AID Safety load 400 KW 4) NON-Essential load 200 KW 5) Other service loads 200 KW Calculate and suggest the size of the transformer, size of main cable, capacitor bank, and calculate the capacity of an emergency load having above first three mentioned loads is supplied by an emergency generator.
How to convert resistance value at 20 degree to 90 degree?
sir, i want to know the calculation for find rated current for cable sizes.(both copper & aluminium) with examole. please sir for example: 35sq.mm al.cable is withstands for how many amps? is suitable for 45kw motor?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)