calculate multiplication factor of a trivector meter with
line ct ratio 200/5A, line PT ratio 11000/110V and meter CT
ratio 200/1A and meter pt Ratio 11000/110V.
Answers were Sorted based on User's Feedback
Answer / shyam sunder thakur
The meter in this case can carry up to 40A current only as meter CT rating is 200/1,
Multiplication Factor if calculated is under
Adopted(line) CT Ratio X Adopted(line) PT Ratio
M.F =--------------------------------------------------
Meter CT Ratio X Meter PT ratio
200/5X11000/110
=----------------------------= 1/5=0.2
200/1X11000/110
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / k.prakashchandra
If the line CT were of 200/1 ratio, the meter would read
correctly. As the ratio is 200/5, for 200 A primary current
the sec current will be 5 A instead of 1.0 .Hence you have
to divide the reading by 5 ,if it is capable of taking 5A.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / ajaz kirmani
Multiplication Factor MF = [ (200/1)x(11000/110)]
-------------------------------
[ (200/5)x(11000/110)]
MF = 5
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / jaskanwar
In a CT PT connection if there is a LTCT meter of 200/5 installed instead of HT meter of -/5 A . Then what will be the MF for this situation.
CT PT = 10/5 A
| Is This Answer Correct ? | 0 Yes | 3 No |
1.Why use in ups in software's,reason,and pls explain. 2.what is the isolation transformer and main use it's functioning and partes.
what is IP55,IP65
Can i use to 3 phase 4 wire energy meter inplace of 3 phase 3 wire energy meter ?
what is high tension ? specify the range?
in VFD when freq is reduce the voltage will reduceor not if it will reduced upto ...
We are having a 2000KVA DG set. It trips with Over speed and Engne Hot when the mahine is stopped in full speed. How shall I analyse the block load and reverse power.Is the problem related to power factor. The machine which runs on this DG is having all Synchronous motors with incividual Drives.
WHY IS THE NO LOAD CURRENT SMALL FOR A TRANSFORMER COMPARED TO OTHER ROTATING ELECTRICAL MACHINES??
how can we judge the percentage of load on the basis of temperature differences readings between WTI and OTI in a transformer
What will happen if DC supply is given on the primary of a transformer?
what type of protection and safety req. in the 220kv substaion and area around the substation
what is the minimum clearance between a 11KV 150KVAR capacitor cell and series reactor.can a series reactor can be mounted in the same structure of the capacitor cells structure
WHAT is the no of starts/hr for 3.3 KV, 300 KW motor. Motor is vertical flange type.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)