calculate multiplication factor of a trivector meter with
line ct ratio 200/5A, line PT ratio 11000/110V and meter CT
ratio 200/1A and meter pt Ratio 11000/110V.
Answers were Sorted based on User's Feedback
Answer / shyam sunder thakur
The meter in this case can carry up to 40A current only as meter CT rating is 200/1,
Multiplication Factor if calculated is under
Adopted(line) CT Ratio X Adopted(line) PT Ratio
M.F =--------------------------------------------------
Meter CT Ratio X Meter PT ratio
200/5X11000/110
=----------------------------= 1/5=0.2
200/1X11000/110
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / k.prakashchandra
If the line CT were of 200/1 ratio, the meter would read
correctly. As the ratio is 200/5, for 200 A primary current
the sec current will be 5 A instead of 1.0 .Hence you have
to divide the reading by 5 ,if it is capable of taking 5A.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / ajaz kirmani
Multiplication Factor MF = [ (200/1)x(11000/110)]
-------------------------------
[ (200/5)x(11000/110)]
MF = 5
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / jaskanwar
In a CT PT connection if there is a LTCT meter of 200/5 installed instead of HT meter of -/5 A . Then what will be the MF for this situation.
CT PT = 10/5 A
| Is This Answer Correct ? | 0 Yes | 3 No |
can we start a 6.6kv ht motor with 415 lt supply
in breather of transformer how sillicon gel absorb the moisture?wat happen when the moisture in that oil?
what happen if we give 220 volts dc supply to d bulb r tube light?
what will happen if a part of primary winding of a transformer is accidentally short-circuited?
What are the details of ratings of different types of ACSR conductors?
What is Tan Delta Test
What is the need of ISOLATION Transformer?
how much LT load can bear by the 100 KW HT connection.
When should I use earth leakage circuit breaker for incomer and when should I use it for each feeder seperately?
what is excitor response of an excitor?
sir, Two different rating of generator going to connect parallel, can it set same DROOP or different. Why? Please explain
As per principle we say in three phase supply ,the voltage is producing by phase angle between two phase so two phase is needed means then why we using three phase ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)