How can decide the MVA rating of power transformer for
substation like 220/132, 132/66, 66/33kv etc or even higher
kv rating of substation????
Send me the strictly technical answer that shows your strong
technical aptitude.
Answers were Sorted based on User's Feedback
MVa Rating is Depends upon the Load when Load is
increased current will increase so we design for different
rates of Mva Depends upon the load
S= 1.732* V*I for Ex 50 MVA
50* 10^6 = 1.732* 220* 10 ^3*I To Calculate the I Value
is 131 in Hv side Lv side 218 A
Is This Answer Correct ? | 23 Yes | 4 No |
The MVA rating is only based upon the generating MW capacity
of the plant.
For Example:
50MW is generated in the Powerplant.(i.e. Generator
capacity is:50MW,11kV,0.8P.F,3000RPM)
Now we like to connect this 50MW power to the E.B.grid
then we use one Step UP Transformer i.e. to step up the
voltage from 11kV to 220kV.
Now we can calculate the MVA rating of that step up
transformer as:
i) MVA = MW/costeta
MVA = 50/0.8 = 62.5MVA.
This is the answer.....
By,
Karthik(Engineer)
Is This Answer Correct ? | 11 Yes | 7 No |
Answer / srikanth.kondru
very simple
we need to know the Load of the sub station ..
for example it is 1000 H.P
as we know that 1 H.P =1.5 amps
voltage is 220 KV
power ,p = 746KW = 1.732*0.8*220KV*I
I = 746 KW/1.732*0.8*220KV
= 2.4 amps
S=220*2.4*10^6 =532 MVA
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / milinda4p
The MVA rating of a power transformer depends on the load
connected to the transformers. this can be calculated (for a
grid transformer) by calculating the total MVA of the
primary substation transformers connected to it.Generally
this is calculated with a extra space for load connection.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / k.prakashchandra
The present load and anticipated load growth in the coming
10 years.
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / raju
transformer is working only based on load. frequency was not changing, so it is called mva
Is This Answer Correct ? | 2 Yes | 6 No |
Inductor and capacitor........power in one phase and ...... in it another phase.
what is the basic difference between capacitor and condenser ?
in DG synchronization system can i short R,Y,B- phase(DG-1) to R,Y,B Phase (DG-2), HOW IT WORK . WHAY WE NEED TO SYNCHRONIZATION.
what is dc mator?types of dc motor?losses in dc motor?what is the mechanical,electrical and commercial efficiency of a dc motor?
Can anybody inform me about the pattern of ECIL GET( Graduate Engineers Trainee) interview for Electrical students? Will there be HR round as well? I thought of preparing for 2 to 3 subjects thoroughly. Will it be sufficient? Please share your thoughts.
what is VFD and where is use of it
cb used in railway applications is?
Can u tell me design of switch yard
The synchronous speed of a motor with 6 poles and operating at 50 Hz frequency is ___.
Is necessary Protection CT, CLASS - 5P10 fitted at Incomer side of main Breaker ? Why ?
What is rated value? is it phase values or line values?
Why Water motor is not taking a load or pressure while everything is correct. (Note: Motor running properly)