when we are using HART COMMUNICATOR why we are using 250 ohm
resistance while using HART COMMUNICATOR.

Answers were Sorted based on User's Feedback



when we are using HART COMMUNICATOR why we are using 250 ohm resistance while using HART COMMUNICAT..

Answer / sivakumar d

Its Ohms's Law:

We need output: 4 to 20mA. corresponding voltage level is 1-5V

when Min Transmitter O/P

I=V/R =1/250 =0.004 =4mA

When Max Tranmitter O/P
I=V/R =5/250=0.02 =20mA.

So to get Standard Current Signal We need 250 ohms resistor.

Is This Answer Correct ?    15 Yes 3 No

when we are using HART COMMUNICATOR why we are using 250 ohm resistance while using HART COMMUNICAT..

Answer / anees

Because that Hart Calibrate need proper loop resistance
there for when we use in lab/Bentch calibration we need
it,otherwise in field calibration we doesnot needed

Is This Answer Correct ?    18 Yes 10 No

when we are using HART COMMUNICATOR why we are using 250 ohm resistance while using HART COMMUNICAT..

Answer / vinodkumar

when calibrating an hart transmitter in lab, we need a loop resistance between 250 ohms & 600 ohms, because without a resistor the HART communicator did not communicate with the transmitter. Because transmitter is a high impedance circuit with respect to the HART communicator. When HART communicator try to communicate with transmitter by producing a digital signal, the signal gets grounded through power supply and thus the signal didn't enter the transmitter without the resistor. When resistor is added, the transmitter become a low impedance circuit with respect to the resistor, so the signal produced by the HART communicator SHOULD have pass through the transmitter and so does the communication between HART communicator and HART Transmitter. Without the resistance between 250 ohms and 600 ohms the HART communicator did not communicate with Transmitter.
But in analog transmitters exact 250 ohms is used to convert 4 - 20mA to 1 - 5V respectively. For this only and exact 250 ohms is needed

Is This Answer Correct ?    5 Yes 0 No

when we are using HART COMMUNICATOR why we are using 250 ohm resistance while using HART COMMUNICAT..

Answer / md. afroz alam

To increase the loop of Resistance we use 250 ohms Resistance with smart transmitter in bench or lab calibration

Is This Answer Correct ?    0 Yes 4 No

when we are using HART COMMUNICATOR why we are using 250 ohm resistance while using HART COMMUNICAT..

Answer / g.ramesh

because of the load impedence it should need the 250
resistor at time only we are able to get the frequency
of 1200hz to 2200 hz

Is This Answer Correct ?    3 Yes 9 No

when we are using HART COMMUNICATOR why we are using 250 ohm resistance while using HART COMMUNICAT..

Answer / imran

According to Ohm Law V=IR .we need resistance for voltage
drop across Hart as current is there to energize Hart
circuit.and due to hart hat low impedence w.r.t XTMR .DCS
Cards hav builtin resistance that s why no need for
resistance in field

Is This Answer Correct ?    2 Yes 8 No

when we are using HART COMMUNICATOR why we are using 250 ohm resistance while using HART COMMUNICAT..

Answer / sandip

we r using 250 ohm resister to convert 4-20 ma output.

Is This Answer Correct ?    5 Yes 12 No

Post New Answer

More Instrumentation Interview Questions

on interface level transmitter model(RTG3302-EMERSON) What is threshold valve how can we select correct threshold value T1,T2,T3,T4 When interface water & hydro carbon

0 Answers  


how to design orifice plate?what is the equation?

0 Answers   REL,


what is Best Among SINK Or SOURCE Type Design In Digital Signal, Either Iput Or Output? WHY?Can any one..

0 Answers   Accer, Reliance,


EXPLAIN NETWORK COMMUNICATION ON DCS?

0 Answers  


pls any1 sugges me book for plc,dcs & scada..

1 Answers  






what is the calibration procedure for transweigh make weigh feeder?

0 Answers   Anjani Cements,


what is zero trim and span trim?. at which problem we need to use this?

3 Answers  


I want to know the questions asked in ONGC interview(after being selected in the written exam) for Instrumentation branch.Kindly help.

0 Answers  


A differential transmitter is calibrated to measure the flow of lquied, explain what wil happen if the fluid is not pure but contains some bubble?

2 Answers  


why 1 to 5 vdc is used for output measurment

4 Answers  


what is the deference bitween DCS and PLC SCADA HMI System for Power Process Industry.

1 Answers   UltraTech,


i need some objective type questions in instrumentation

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16631)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1094)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)