how to measure temperature from resistance of rtd?and how to
measure temp from voltage of thermocouple?is there any formulas?
Answers were Sorted based on User's Feedback
Temperature measurement.
With RTD:
The Material used Is Platinum Which is very Sensitive to
the temperature as the temperature Changes the Resistance
changes.Which is next connected to form a Weatstone bridge
in the transmitter then According to the formula
R1/R2=R3/R4 since R2,R3,R4 are Constant So Change in RTD
Resistance R1 The Corresponding mA Signal is Obtained
through the transmitter to the system in control room.
With T/C:
Were As T/C is the Formation of two diffrent Material
Combined to form a T/C(SEEBACK EFFECT)As they r two
different materials Change in temperature Causes the change
in EMF generation between the two materials,This mV Signal
is then Transmitted to Marshelling cabinet to Convert it
into V because all Digital Signal read minimum 5V,it is
Converted by OP-Amp with 250ohm Resistance Across it whict
is convinient to DCS to read it.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / nishat
to measure temperature through RTD there is a formula T=(R-100)/.385
FOR PLATINUM RTD rise in 1 degree there is increase of 0.385ohm resistance
about T/C IF ANYONE KNOW SO PLEASE DO ANSWER
| Is This Answer Correct ? | 0 Yes | 0 No |
During the measurement of Temperature from RTD, we have to
just disconnect the RTD from the control room,(as it is
externally powered, in case of thermocouple it is self
powered transducer) after disconnecting just measure
resistance of element e.g. 115 ohms.. then deduct 100 from
it...you will get say 15,,,then multiply this by 2.5..you
will get the temperature ,,approximately you will get 38
degrees..
| Is This Answer Correct ? | 0 Yes | 4 No |
can u please give the exact ckt explaination of AC Drive related to industries.
how to calibrate and troubleshooting of leveltroll?
What is the constant voltage unit?
Why we use negetive (-)voltage in vibration system
When can a bypass not used on a positioner?
what's meanning of 1250KVA and how to calculate with Volttage and Current. answer give with example.
difference between vaccum and draft
Why we are using temperature and pressure as a reference when measuring flow of steam?
What is the basic principle of vibration measurement by BENTLY NEVADA vibration measurement system? and Why it gives the -ve voltage output?
14 Answers Ensol, GNFC, Reliance, Siemens,
Why the tapping connections are taking above for gas service and below for liquid service?
Hello Friends do you know this answer of this Question? Which color you would use when there is Somthing not correct or need to change In P&ID? i mean color that use for highlight that need to update in P&ID. Yellow Highlighter ? Red color ? Blue Color ? Appreciate for your answer. Thanks Blue Color
If the on Of the DO module is off in the System cabinet, then what is the Procedure to check weather the Module is working or not.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)