how to measure temperature from resistance of rtd?and how to
measure temp from voltage of thermocouple?is there any formulas?
Answers were Sorted based on User's Feedback
Temperature measurement.
With RTD:
The Material used Is Platinum Which is very Sensitive to
the temperature as the temperature Changes the Resistance
changes.Which is next connected to form a Weatstone bridge
in the transmitter then According to the formula
R1/R2=R3/R4 since R2,R3,R4 are Constant So Change in RTD
Resistance R1 The Corresponding mA Signal is Obtained
through the transmitter to the system in control room.
With T/C:
Were As T/C is the Formation of two diffrent Material
Combined to form a T/C(SEEBACK EFFECT)As they r two
different materials Change in temperature Causes the change
in EMF generation between the two materials,This mV Signal
is then Transmitted to Marshelling cabinet to Convert it
into V because all Digital Signal read minimum 5V,it is
Converted by OP-Amp with 250ohm Resistance Across it whict
is convinient to DCS to read it.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / nishat
to measure temperature through RTD there is a formula T=(R-100)/.385
FOR PLATINUM RTD rise in 1 degree there is increase of 0.385ohm resistance
about T/C IF ANYONE KNOW SO PLEASE DO ANSWER
| Is This Answer Correct ? | 0 Yes | 0 No |
During the measurement of Temperature from RTD, we have to
just disconnect the RTD from the control room,(as it is
externally powered, in case of thermocouple it is self
powered transducer) after disconnecting just measure
resistance of element e.g. 115 ohms.. then deduct 100 from
it...you will get say 15,,,then multiply this by 2.5..you
will get the temperature ,,approximately you will get 38
degrees..
| Is This Answer Correct ? | 0 Yes | 4 No |
what is difference between Floating D.C.Voltage and Fixed D.C.Voltage?
The pressure class rating (such as 150 lb, 300 lb, etc.) of a line appears in the form of ________________ in the Line Number (or Line Designation) on a P&ID
what is the meaing of calibration curve?
what is absolute pressure, gauge pressure and atmospheric pressure?
what step is taken for ESD ( emergency shut down) in DCS REPLY to hashimka20009@gmail.com
0 Answers Bosch, Eskom, Sabic,
why we use -ve voltage in vibration monitoring system.generally we use 4 to 20 mA as output of instrument then why we use voltage in vibration
how to calibrate the radar transmitter for measuring the exact tank level if tank is having agitator moving continiously because due to agitator tank surface level will vary every time.
Can anyone send most commonley asked Instrumentation questions and answers in cement industry please?
HOW TO CALCULATE ACCURACY OF AN INSTRUMENT. WHICH IS COMPITABLE FOR USE.
when the force applied on load cell the ohms will be varriying .and how its convert ohms to mv generate and have any formulae?
1 Answers UETCL Uganda Electricity Transmission Company Limited,
Boiler flame scanner advantage?
0 Answers Fluke, Petrochemicals, Tata Chemicals,
pls send me the 10 years technical question papers of NTPC AND BHEL
15 Answers Bhel, NTPC, ONGC, UCE,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)