how can you set a zero and span of transmitter?
Answer / bunny
First give the LRV(Lower Range Value)to the transmitter.If
it is an electronic transmitter,the o/p should be 4mA.If it
is a pneumatic transmitter,the o/p should be 3psi.If we are
not getting the above values,adjust the zero screw in the
transmitter by a screw driver,till we are getting 4mA or
3psi.This is called zero adjustment.Simillarly give URV
(Upper Range Value) to the transmitter.So the output for
electronic and pneumatic transmitters should be 20mA and
15psi respectively.If we are not getting it,adjust the span
screw in the transmitter by a screw driver till we are
getting 20mA or 15psi.This is called span adjustment.
LRV & URV:Suppose the range of a transmiter is 0-30psi.Then
LRV=0psi & URV=30psi.
| Is This Answer Correct ? | 23 Yes | 0 No |
How flow control valve is working with pnuematic positioner and I/P convreter from command is given from remote
why the SCAN time of DCS is more & that of PLC is less? if the SCAN time of DCS then why we use DCS.
What pressure results for a flow transmitter of range 0- 180t/h in the dcs and 0-301mbar in the field using square root extraction. Kindly also suggest formulae for the percentages 0,25,50,75,100?
Can any body give detail about orifice sizing?
PT RTD Range: -200 to 500 degree celsius If I configured in DCS Lower range and Upper range . In face plate it shows red colour due to overa range how was the characteristics look If the temperature is more than operating range. how was the characteristics look . whether its in Resistance vs Temperature curve is Linear or Non linear
if i want buy a pressure gauge then witch parameter i look
Working principle of magnetic flow meter ......and calibration procedure of e+h magnetic flowmeter...
What are the processes Variables?
what is effect of specific gravity in differential level transmitter , explain formula related with this .
0 Answers Flour Tech Engineers (P) Ltd,
why we are using digital signals for I/O & how to measure this signals is getting or not ?
what is difference between PLC and DCS?
Displace type LT to be calibrated in workshop, wt. 40, dia- 60 mm, density- 0.8kg/cm3.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)