Answer / bunny

First give the LRV(Lower Range Value)to the transmitter.If
it is an electronic transmitter,the o/p should be 4mA.If it
is a pneumatic transmitter,the o/p should be 3psi.If we are
not getting the above values,adjust the zero screw in the
transmitter by a screw driver,till we are getting 4mA or
3psi.This is called zero adjustment.Simillarly give URV
(Upper Range Value) to the transmitter.So the output for
electronic and pneumatic transmitters should be 20mA and
15psi respectively.If we are not getting it,adjust the span
screw in the transmitter by a screw driver till we are
getting 20mA or 15psi.This is called span adjustment.
LRV & URV:Suppose the range of a transmiter is 0-30psi.Then
LRV=0psi & URV=30psi.

Is This Answer Correct ?    23 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

What is the processor scan time of allen bradle control logix processor 5555 lenin lenin123us@rediff.com

1 Answers  


What are the logic behind 2x2 and 2x3 logic and more when ask in interviews

1 Answers   Reliance,


What different types of problems do occur while doing the loop checking? and please explain in detail or mail me at kadam.aniket143@gmail.com

1 Answers   Operational Energy Group, Process Control Technologies,


what will be the pressure in tank which has the total level of 2 meters and is filled 1.2 meters ?

4 Answers   Engro,


What is the difference between floating and fixed voltage?

1 Answers  






What is the working principle of oxygen analyzers(zirconium oxide type) used in CFBC boilers?

3 Answers   Bajaj, Kohinoor, Wartsila,


what is control valve and how is work

5 Answers   Descon,


how to connect the HART protocal with control valves

1 Answers  


1. what is 3 point calibration & 5 point calibration? 2. If we use hart communicator to set the LRV & URV of a smart transmitter, did we calibrate the transmitter? why? 3. Make a complet list if meterials needed to properly connect a pressure gauge to a steam pipe using 1/2 inch stainless steel tubing. The gauge connections is 1/2 inch NPT-M and the steam pipe tap has a 1/2 inch female coupling, compression fittings are use. 4. What are the tools in loop checking? 5. What would the ISA symbol of a square root extractor look like? 6. What would you do to completely prepare for the configuration? 7. What safety measures must you undertake when doing configuration? 8. what are the two most commonly use programming languages used when we configure a PLC? 9. What would you do if you accidentally skipped a step in the configuration procedure? 10. How would you know if the configuration were sucessful? 11. Name at least 3 selections available when we configure the burnout protection of a controller?

3 Answers   EI Electrotechnical Institute,


Wht is Dry Leg Calibration and Wet Leg Calibration?

2 Answers  


how checking is done in fiber optic cable? explain the working of RTU?

5 Answers   PSU,


how the actually positioner of control valve working? where we gave 3-15psi pressure to I/P converter where it is firstly applied ?- on I/P to positioner then what happen? is control valve operate on 3-15 psi or its bench pressure?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)