findout of current?details 440v,3phase,085pf,hp-5
Answers were Sorted based on User's Feedback
Answer / sonali
7.5amps
GENERALLY WE TAKE 1.5 TIMES OF H.P
5*1.5=7.5A
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / naresh
rating =5*0.7457 =3.7285kw
vol =440v
3phase
current=(3.7285*1000)/(1.732*440*0.85) =5.755A
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / meraj
Given: v=440v, 3phase, pf=0.85, hp=5hp I=?
1hp=0.746kw
5hp= 5*0.746 kw = 3.73 kw
now P=3.73kw
for 3phase P=1.73*v*i*pf
I= P/(1.73*V*PF)
I = 3.73*1000/(1.73*440*0.85)
I = 5.76 amps
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / siva
power=1.732VIcos Pi
Hp to Kw
5x746=3730
I=3730/1.732*440*cos 0.85
I=4.89 A
Is This Answer Correct ? | 0 Yes | 8 No |
Answer / jim
p=vicos0
p=5*0.746
=3.73kw
i=3.73/(440*0.85)=9.973amps
Is This Answer Correct ? | 2 Yes | 11 No |
can we use ZNyn11 transformer instead of Dyn11 transformer in distribution for effectively eliminating harmonics from the industrial loads.
We are designer please help me calculate the size of 11kv cables from step up transformer to M.V panel, total load is 5 mega watt distance 900 feet (used aluminum type cables) please provided formula for calculate the cable with example.
why do select 11000v rubber mat even we use only 415Volts
1 Answers Saint Gobain, Tata Steel Limited,
Why (In India) we preferably go for +-30 deg connection of transformer? what are the advantages in this connection?
Explain the propagation of harmonics in the network and influence of phase angle of harmonics.
A Question Like A Wire Is Wound Whose Resistance Is Some 132. 44647 Ohms. If A Voltage Of 30 mv, 296 Ma Current Is Applied To It What Is The Resistance.
Can transformer develop three phase power from a single phase source?
140 is load amps for a equipments and what ratio of CT requied for installimg ammeter to amps montering purpose?
Can we use delta-star neutral grounded 3 phase power transformer bi-directionally.
is it possible to test of bus bar in high rise building without completed full floor ?
Just a silly question but just to make my curious mind bac to normal - Why was not 67 and 67N relays built into a single relay as i have noticed that the R,Y,B CT wiring end up into the 67 relay while the common of the R,Y,B CT wiring end up into the 67N relay. Then it was better if a single relay was manufactured just like the distance relay (21). Another question i would like to ask is - how do we know where the 67 and 67 N relay has to be placed.why is it not placed at the transformer bay? In the substaion that i am working -i have noticed that it is placed between a breaker and a common double bus bar and this line bay is connected to another substation at a remote place which is furthur connected to a load. B U S______CT for 67 & 67N ______Breaker _____ remot s/s. B A R
I want to replace the 3 KW DC motor with AC motor so what should be the rating of AC motor? Details Of DC motor to be changed with AC are - Kw - 3, Vf - 310, If - 0.15, Va - 400, Ia - 13, RPM - 2400