We have two 1 phase heating coils having same resistance
of 25ohm, but during operation one takes 3A and other 6A
Is it posiible Pls. explain
Answers were Sorted based on User's Feedback
Answer / arvind
Yes it is possible,if two coils have same resistance but
supplied voltage is different as 75 v for 3 A and 150 v
supply for 6 a coil. from ohm's law.
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / man
even when applied voltage to both the coils are same we can
have different currents.as because the inductance of both
the coils can be different(since its single phase supply so
inductance will come into picture,which depends on the
dimension of the coils),so the impedance of the coils will
be different and hence currents will be different even for
same voltage.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / mohseen ahmed
according to ohms law V=IR......if voltage is contant then
there will b constant current following through
resistance..but if supply voltage is not constant then load
current may b different....i hope u got the answer...REGARDS
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / k.prakashchandra
The coil wound over an insulted iron former will draw less
current.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / noel c. tigas
Answer # 3 is incorrect. We need to analyse the statement.
Heating coils are surely resistive, hence, we can eliminate
inductance. Answer no.#1 is the correct answer. They
should have different power ratings; hence, their operating
voltage, also the formula P = Square of I x R.
| Is This Answer Correct ? | 0 Yes | 1 No |
What are the significant parts of dc generator?
How vfd saving power.
Unit of Magnetic Flux Density a) Tesla b) weber c) Hendry d) Farad
What is the working of SCM CT or purpose in genrator ?
How much should be the load percentage for 15kva Inverter and Iinut & I output load with Calculations
When measuring the Insulation resistance of a motor winding (winding to earth) using a megger meter, Applied voltage(1000V) was automatically reduced to 500V. and the measured insulation resistance values are also very low (in Kohm range) Can anyone give me a reason???
What is minimum phase system?
How to select the ratio of neutral ct? Is there any relation in between percentage impedance and neutral ct ratio ?
How power factor of electric system improved?
What is a differential amplifier?
What is the meaning of TRI Vector meter?
7 Answers ABB, Excel Power Switchgear,
A 500 V shunt motor runs at its normal speed of 250rpm when the armature current is 200A. The resistance of the armature is 0.12 Ω. Calculate the speed when a resistance is inserted in the field reducing the shunt field to 80% of normal value and the armature current is 100A.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)