What does CDG,CDAG,CAG,VAJ,VAJH,VTT,VAZ,VAA etc. stands for
in case of relays and can anyone answer to decode this
codes C,V,D,G,A,X,TT,J,JH etc
Answers were Sorted based on User's Feedback
Answer / rajan singh tanwar
This is based on
very simple
concept:-
It has three
letters and they
are coded as
follows:-
First Letter -
Operation
Quantity
A - Phase angle
comparison
B - Balanced Current
C - Current (Amps)
D - Differential
E - Direction
F - Frequency
K - Rate of rise of
current
M - Manual
O - Oil Pressure
P - Poly phase VA
R - Reactive VA
S - Slip Frequency
T - Temperature
V - Potential
W - Watts
X - Reactance
Y - Admittance
(Conductance)
Z - Impedance
Second Letter -
Measurement
A - Attracted
armature
B - Buchholz
C - Induction
D - Induction Disc
G - Galvanometer
I - Transmitter
J - Mixed Types
M - Magnet
(polarized)
P - Plug
R - Rectifier
S - Synchronized
Motor
T - Transistor
W - Weight (Gravity)
Third Letter -
Application
A - Auxiliary
B - Testing
C - Carrier or
Counting
D - Directional
E - Earth/Ground
F - Plug or Alarm
Indicator
G - General or
Generator
H - Harmonic
Restricted
J - Tripping
JE - Tripping
(Electrical
Reset)
JM - Tripping
(Manual
Reset)
JS - Tripping (Self)
JC - Tripping
(Conductor)
K - Check Alarm
L - Local Limiting
M - Same Phi or
motor
N - Negative
Sequence
O - Out of Step
P - Potential
Failure
R - Re-closing
S - Synchronizing
T - Timer or
Transformer
U - Definite Time
V - Voltage
Resistant
W - Piolet Wire
WA - Interposing
WS - Inter-tripping
X - Supervisory
Y - Flash Back
(Black
Fire)
Z - Special
Application
Z0 - Zero Sequence
Examples :
CDG - Current
(operation
), Disc
(Measurement),
General Purpose(
Application)
CAG - Current
(operation
), Attracted
armature(
Measurement),
General
Purpose(Application)
VAJ - Potential
(operation
), Attracted
armature(
Measurement),
Tripping(
Application)
VTT - Potential
(operation
), Transmitter(
Measurement),
Transformer
(Application)
VAZ - Potential (
operation),
Attracted
armature
(Measurement),
Special Application
VAA - Potential (
operation),
Attracted
armature
(Measurement),
Auxiliary
(Application)
Thanks I hope it
will help you.
Rajan Singh Tanwar
J.K.Cement Ltd.
| Is This Answer Correct ? | 163 Yes | 6 No |
Answer / tawumap ent
the first letter account for what is to be measured
the second letter is for the type of what causes the movement
so for the C part its for Current, for the V part its for
Voltage
The D is for disc operated. If u go and look closely on the
relays you will find an induction disc contained therein.
The other letters im going to figure out and tell you
| Is This Answer Correct ? | 60 Yes | 8 No |
Answer / k.prakashchandra
To add (As I remember)a few more. A- attracted armature
(Instantaneous), G- general purpose, H- high rupturing
capacity ( heavy duty),J- master trip,T- with timer and Z -
impedance
| Is This Answer Correct ? | 22 Yes | 9 No |
Answer / mithun mesta
J- Dc In comer
K- control,closing, Tripping
L- Alarm,Annunciation,
E- Potential Tranformer
H- AC supply
C- Protection Circuit
D- Metering Circuit
A- CT secondary for special protection
| Is This Answer Correct ? | 16 Yes | 22 No |
what is self commutation how a thyristor discharges through a capacitor and inductor
how can a race around condition be eliminated using master slave flipflop?????
We use MCCB not MCB for motor starters because MCCBs has capablity to drawout the motor starting current which is 5-6 times the full load current of motor for 1sec. Then why we use SDF in starter panel means MCC panels. Pls reply if any one knows this answer.
state application of relay in transmission line?
How to convert 2 phase to 3 phase electricpower in induction moter?
how to calculate the voltage drop in electrical cable while laying cables?
Why VL is more than the Vc?
why generator efficiency is more in swinburnes test?
If there is volagte between earth and neutral, what should be the reason ? and solution * What should be allowable limit in case, if the voltage between earth and neutral exist ? / OR what is limit for safe voltage between earth and neutral?
I have 200 KVA Isolation Transformer for UPS input side. & ups was having 48% load, suddenly got short what will be the reason.
how to calculate P.F from kva only?
Why does the rotor rotate?
1 Answers Machino Polymers, OPTCL,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)