We use MCCB not MCB for motor starters because MCCBs has capablity to drawout the motor starting current which is 5-6 times the full load current of motor for 1sec.
Then why we use SDF in starter panel means MCC panels.
Pls reply if any one knows this answer.
Answer / omer a.osman
What do you mean by SDF. I guess Star/Delta.
In this case, the starting current will be reduced & within 15 to 20 Sec. the Sytem will changed to Direct on line in running Condition by taking the full load current. Hence, the recommended MCCB rating as protective device to protect the feeders should not be less than the current carrying capacity & tripping current about 1.45In. However, the breaking Capacity of the MCCB is an essential factor.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the name of the oil is used in transformer?
briefly explain the main blocks found in a microprocessor based system
fog produced due to?
in alternator what is use of AVR ? how AVR is operating either AC or DC?
What the full form of KVARs
What is the basic difference between earthing, ground and neutral?
Describe the control mechanism of missile launcher???
what happens when we give supply to the secondary of a transformer ?? for example 415v(pri)/110v(sec)
How do you select a cable size(Cu & Al) for a particular load?
What is the battery voltage limit
how can we can take BDV test in transformer?
what is the meaning of impedance protected in instrument cooling fan
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)