hi sir i have load of 17.5kw in 3 phase lighting circuit which
mcb i can use
Answers were Sorted based on User's Feedback
Answer / a.s
there is a formulae for 3 ph.
p=root 3vicos0.8
by that formulae we can get nearly 35.2amps so we can put
40-50amps mcb
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sujit
18*1.73*1.3=40Amp
Here we Have Consider 13% sc current.
50 Amp MCB is Not Easily Available in Market. so Better you use 63 Amps MCB.
Is This Answer Correct ? | 2 Yes | 0 No |