what is the meaning of transformer short circuit test?
Answers were Sorted based on User's Feedback
Answer / amal
The short circuit test is performed by short circuiting one
of the two windings, by supplying the other one with a
voltage adjustable from zero, until reaching the value of
the rated current of the winding itself. The voltage
required at this purpose can be of the order from 4 to 10%
of the winding Vn on which we perform the power supply; such
a voltage is defined short circuit voltage of the
transformer. In this test, the whole absorbed power
corresponds to the only copper losses of the two windings,
since, the low applied voltage given (in the short circuit
test of the transformer), the magnetizing current, the flux
in the core and the consequent losses are negligible. In
these conditions we determine the equivalent resistance of
the transformer.
In turn we will therefore be able to determine the
variations of the secondary voltage that take place from no-
load to load condition of the transformer itself. Even in
this test it is indifferent to supply the primary or
secondary winding. In practice it is necessary to consider
that it is suitable that the involved currents reach the
tayed value of full load both in the side of the supply
winding and in the other short circuited one. The first
value will be necessary for the instrument choice, while the
second one for the choice of the cable section to be used on
the short circuit connections.
| Is This Answer Correct ? | 20 Yes | 7 No |
Answer / balendu nath pandey
short ckt test perform in transformer for determine the
copper loss. because in short ckt condition voltage does
not present then we easily calculate the copper loss
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / krupa reddy s
sc tect is conducted mainly to check the dynamic and
thermal withstanding capacity of the transformer (because
in some worst cases there may be chance of short circuit in
the power system or transformer)at the same time they find
out load losses also.....
Procedure-LV side Shorted
Hv side- current is applied,
normally 9 shorts will take,
and one thermal short
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / rajan
short circuit test is done to find full load parameters of
transformer like efficiency,etc.
| Is This Answer Correct ? | 5 Yes | 3 No |
ACTUALLY WE DETERMINE THE COPPER LOSSES BECAUSE COPPER LOSSES ARE BASICALLY EFFECTED TO THE EFFICIENCY
THE VALUE OF THE CURRENT IS VARIED ACCORDING THE LOAD SO THAT MINS BUT IN CASE OF THE TRANSFORMER THE both losses are not depend on the phase angle
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / karthick
transformer short circuit means to check transformer for its
efficiency ,,,, over load protection
| Is This Answer Correct ? | 4 Yes | 6 No |
IN THE SHORT CIRCUIT TEST WE DETERMINE THE COPPER LOSS .IN WHICH SECONDARY SIDE OF THE TRANSFORMER(LOW SIDE OF THE TRANSFORMER ) IS SHORT CKT BY THE AMMETER AND RELAY AFTER THAT WE APPLY RATED CURRENT ON THE HV SIDE OF THE TRANSFORMER AND HV SIDE A SMALL VOLTAGE ARE APPLY WHICH IS 2 TO 10% OF THE RATED VOLTAGE .SO THE VALUE OF THE VOLTAGE IS VERY LOW AS COMPARE TO THE FULL LOADED VOLTAGE .SO READING OF THE WATTMETER ARE ONLY THE READ THE VALUE OF THE COPPER LOSSES AND ALSO DETERMINE THE SHORT CKT PARAMETER Rsc , ZsC AND ALSO Xsc
| Is This Answer Correct ? | 1 Yes | 3 No |
how you can select circuit breaker for 2000kva transformer?
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
UPS battery Back time = no.of Batteries * Ah of the Battery / output KVA * 130 ? what is the 130 means ? can any one help? because all are using this formula how its came 130?
How Negative Phase Sequence Relay works in case of Synchronous Motor?
I want to know the principle of rotating flux transformer.
what is differant beetween overload current and phase current?
WHAT HAPPEN WHEN CT SECONDARY OPEN DURING LOAD
can we use relay in fan?
Please elaborate th´evenin’s theorem?
What is EHT(Abrebiation,Function,Voltage Regulation & how it works?
Why indicated only R.Y.B to phase.
What is the formula to find out two phase active & reactive power
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)