what is fault level of power system ?
Answers were Sorted based on User's Feedback
Answer / dhiraj shringi
the power upto the fault in power system is known as fault
level power.
it is calculated by the following formula:
fault MVA= BASE MVA/PU IMPEDANCE upto fault level.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mahesh sali
As per IEC std. Low voltage fault have decide as below
mentioned ranges.
For 50 KA / 65 KA at 1 or 3 sec.
for cal Fault current KA - ( KVAsc/ %sub transient
reactance ) *100
thanks
| Is This Answer Correct ? | 0 Yes | 0 No |
The potential difference between a phase and neutral is 230v , but the potential difference between two phases is 400v. why?
in a refinery one motor is suddenly stoped. what will do how can i findout the problem explain step by step
i am completed diploma in ece,and working in ht and lt lines.so is elligible diploma in ece for get electrical C Licence?plse give ur opinion?
How to get Electrical Supervisory Licence in chennai Tamil Nadu from TNEB. I am BE EEE graduate.
WHAT IS A DIFFERENCE BETWEEN A DC GEAR MOTOR AND STEPPER MOTOR.AND WHICH IS MORE APPROPRIATE TO USE FOR POSITION CONTROL PURPOSE?
why to need a electrical earthing?
What's the differs between voltage & current & emf.
Has someone here done a sizing for a generator (3 phase), its for a pumping station. If you have an example for standby/duty and both running (I) star delta (ii) Soft Starter.
Initially, when the input is not equal to the output — what type of response is this?
1- XC and the RC time constant are both measures of the reaction of C to a change in ____? 2-The power factor is a numerical ratio with a value between 0 and 1 equal to the ______________ of the phase angle. 3-When V and I are out of phase because of reactance, the product of V times I is called ______________ power 4-For _____________ inductors, the branch currents can be added algebraically. 5- The ______________ power in watts can be calculated as I^2R 6-Calculate XL with L = 30mH and f = 1kHz ( I have Xl=2piFL 2*3.141592653*1kHz*30mH =188 ohms Please check) 7-A parallel RL circuit has the values, R = 5kohms, XL = 5kohms. A voltage source of Vt = 10Vrms is connected in parallel to R and L. Determine the total current, It delivered by the voltage source Vt. 8-A series RC circuit has R = 1Mohm and C = 1microF. How long would it take for the capacitor to fully discharge if it is initially fully charged? 9-A circuit has real power = 300W and an apparent power of 500VA. Determine the power factor and phase angle. 10-The time constant for an LR series circuit is T = 0.1s and R = 10ohms. Calculate the inductance L.
We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Make Atlas Copco 5.5 kva) that time we face the lot of fluctuation on Dg output. Can you please suggest me how can prevent this fluctuation?
Why PT voltages are measured with respect to ground? What do u mean by voltage or current polarized.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)