We are using Powerica make 100 KVA DG set. Whenever i
connect compressor on DG load (Compressor Make Atlas Copco
5.5 kva) that time we face the lot of fluctuation on Dg
output. Can you please suggest me how can prevent this
fluctuation?
Answers were Sorted based on User's Feedback
Answer / prajeshkumarbe@yahoo.com
hai to all..,
this is the wonderful question, powerica DG is another
company of Caterpillar .atlas copco also best compressor
designer.
ur Dg is 100KVA , load is 5.5KW (its not a 5.5kva) that
means 7.5 hp,
while getting the fluctuation note it below.,
1.whether fluctuation is comes while starts r stops(loading/
unloading)
2.fluctuation time wt is the pressure (if compressor
reaches maximum working pressure it will takes more current)
3.normally it will be enough DOL Stater ,if its take more
current while start /stop,just u make the Star Delta
stater , surly will get best result.
4.check the DG fuel filter condition ,if its ran above 300
running hrs replace newly
5.DG should be run 80% load max ,
6. give the DG load only compressor itself and measure the
performance
7.ensure the compressor max pressure switch properly working
8.in DG AVR (Automatic voltage regulator) system may failure
9.check the self exciting system rectifier diodes
thanking u all
Rajesh
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajesh
Dear sir,
5.5kva Around (5kw) Capacity is very low
capacity compared to your generator you just calculate
other power usages And load .
If u feel compressor is a only problem you can minimize
other load and start the compressor for testing you can get
conclusion for this issue
Is This Answer Correct ? | 7 Yes | 6 No |
Answer / n. gopala krishna
what type of dg u r using . brushless or brush type if
brush type please check brushes if brushless type check
exitation voltage or some where loose connections in
execitation side
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / elango
the starting current is the only problem which produce a
dip in supply voltage .so higher capacity load must be
started first and next lower loads...
Is This Answer Correct ? | 2 Yes | 2 No |
What is Phase margin?
what is thresold of perception
What are the different sizes of cables for H.T and L.T side of supply?
7 Answers Bhel, BSES, Karthik Industries, Lanco, Nedco, Shilpa Electrical Engineers, TATA, Torrent Power,
Why negative feedback is preferred in the control system?
Why Generator rotate only clock wise ?
when the flux enters into saturation mode then what will be the secondary voltage of the normal t/f?....high or low ? explain ...how?
If I have 3 essential main switch board and 3 incoming electricity ,but only 1 genset running is that possible.
What is line resistance of cable & how it can be measured ?
why elcb used in circuit
A mass of 1200g is accelerated at 200 cm/s2by a force. The value of the force required is:(a) 2.4N(b) 2400N(c) 240 kN(d) 0.24N
I NEED RRB SYLABUS FOR JE ELECTRICAL ,PLEASE SEND TO MY E- MAIL ID joo28_eee@yahoo.co.in
Which of the following can be operated at higher frequencies ? -SCR -MOSFET -IGBT