Why two main buses and one transfer bus scheme not using
for 400kV switchyard
Answers were Sorted based on User's Feedback
Answer / rishi
first of all who told u that main and transfer bus is not used in 400 kv substation.This scheme is used in many substations.
Is This Answer Correct ? | 14 Yes | 2 No |
Answer / naresh.devarakonda
one and half breaker scheme is more reliable, simple
operation and reduces the no. of isolators, bus.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / furqan ahmad
in one and halfbreker scheme scheme both breaker and bus
maintenance is possible.even though this scheme is costly
as compared to other schemes but becoz of reliability and
redundancy it is usually used for 400 kv switchyard
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / jkrocks
DMT scheme is used earlier in 400kV System but all new 400kv ss are made on one & half breaker scheme. it has many advantages over DMT scheme.
more reliable than DMT each time line or ICT remain connected through both buses I & II, reduces numbers of confusing isolator in system, reduce additional bus.
If one bus trip due to any fault , lines are transformer connected to that bus remains charged through another bus by means of Tie CB.
Only disadvantage is that this system require three breaker for 2 lines or transformer.
But It is nothing against lots of advantages of One & Half Breaker Scheme.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / teju
one and half circuit breaker scheme is more reliable than
other schemes, simple operation and reduces the no. of
isolators, some electrical parameters & it is easy to handle.
Is This Answer Correct ? | 0 Yes | 4 No |
3 ph motor connected in star delta starter. when we start the motor it run in star but when in is going in delta it trips the main incoming supply. why?
howmany insolaters needed in 66kv line
we can conformed the vector group of the transformer. How?
whati s the sludge current in ups
what is reactive power?
how and why are capacitors are used to improve powerfactor?
How to confirm the Phase shifting Transformer VECTOR GROUP relation , as below ZNy11.45d10.45-ZNYy0.15d11.15
What's the differs between voltage & current & emf.
3phase motor 400v (induction) A.C 4kw company design 1400rpm but our requirement 2000rpm possible? attached any instrument. reply fast! contact 03343262442
Can you explain about pole discrepancy scheme
Pls tell me what is the exact current conducting capacity of copper and aluminium cables?how much capacity of cables need to 90kw induction motor&how?
How to calculate KW what is the formula for KW.