If we give 2334 A, 540V on Primary side of 1.125 MVA step up
transformer, then what will be the Secondary Current, If
Secondary Voltage=11 KV?
Answers were Sorted based on User's Feedback
Answer / ramendra shukla
As we know the Voltage & current relation for transformer-
V1/V2 = I2/I1
We Know,
VI= 540 V ; V2= 11KV or 11000 V; & I1= 2334 Amps.
By putting thease value on Relation-
540/11000= I2/2334
So,
I2 = 114.5 Amps
| Is This Answer Correct ? | 30 Yes | 4 No |
Answer / nithi
we can't give current to primary side of the transformer
indepedently.
current depends on the secondary side load demand.
| Is This Answer Correct ? | 7 Yes | 2 No |
one 60KVA UPS how can full load current tell me us formulas
what is the meaning of ceiling voltage in Generator exciter?
what is the working principle of energy saver control panel. please give the complete calculation & theory.
The MCB circuit breaker have a voltage rating of 440VAC it's possible to supply a voltage of 480Vac
what mean by machin
What is the most important precaution in any experiment with d.c. Shunt motor?
why the field winding of synchronous machine is excited by dc source
why use delta star x-mer in distribution system.
sir please tell 1 ton equal to how many kilo watt?? in some converter software's that is 3.5 kw. is it right?
what is a power factor?
0 Answers MPWU Kiribati, Thermo,
How can i calculate heat load ?
a starter used for squirrel cage induction motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)