how to check control valve was passing?how to check online?
Answers were Sorted based on User's Feedback
Answer / satya
give 100 % close command to cotrol valve if u phsically check valve is 100 % close the open the downstream drain valve if proces fluid comes then valve is passinf . if theie is flow transmitter before cv u can also check
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / harsh mehta
by zeigler nicols method,,,,,,we can do tht,bro
Is This Answer Correct ? | 2 Yes | 13 No |
what is function of SCADA , and how is it work, explain with difination
0 Answers Bapco Bahrain Petroleum Company,
Sitrans LR460 Radar level transmitter getting level out or disturbed level during moisture present in the material ie coal in the pccb bunker in CHP.Any suggestions for this problem...????
How to interfacing microcontroller with a DC motor
What is differnece between leveltroll and interface leveltrol?
what is exact time to study dcs and plc cources
how to do loop checking pls email to shanavaska2000@yahoo.com
WHAT IS A SYMPTOM OF FAULT WITH THE SPAN OF AN INSTRUMENT? 1)ZERO-POINT AND 100% ARE CORRECT BUT NOT A MID-RANGE. 2)ZERO-POINT IS CORRECT ,BUT 1005 INPUT IS NOT GIVING 100% OUTPUT. 3)LINEARITY PRBS. 4)1005 O/p IS CORRECT BUT ZEO POINT IS WRONG.
if field commnictor 475 does not communicate with transmitter what will you do ?
Is there any temperature compenasation for the air flow from FD fan & SA fans which supplies air to the Boiler?
for commissioning the DPT and Flow Transmitter , what kind of necessary activities we have to check and do? specially that orifice flange valve[ isolation valve}
How to Calibrate Ultrasonic flow Transmitter in Field
what is the difference b/w wet leg & dry leg level method