In a 3Ph induction motor(old) 6 wires came out from terminal
& not mentioned u1,v1,w1,u2,v2 & w2. how can find out the
terminals? how can connect to star delta starter??
first of all you have to use multimeter to identify the
coil teminals. segregate it in two lines as 2 x 3 . ie top
3 terminals and bottom 3 terminals.
Next take a Small DC power supply with 3 volt and a
milliampere meter( DC ). connect this voltage to one of the
coils with milliampere meter in series( Milliampere meter
should be of center zero type ) close the supply voltage to
the coil with make and break it immediately. observe the
deflection whether it is on forward side or reverse side.
and mark one terminal for whcih +ve suplly is connected as
Start and the other ( _ ve )end as Finish. do this
process for other two coils also. once you know the top 3
start points and finish points of the coil. you are almost
there. now you short ckt all finish ends. you are left
with 3 start terminals. ie your STAR connection.
For Delta connection connect finish end of the first coil
to start end of the second coil, finish end of second coil
to start end of third coil and finish end of 3third coil
to start end of first coil. now you have theree junctions.
now your connection is in Delta mode.
| Is This Answer Correct ? | 17 Yes | 2 No |
difference between silent and non silent pole rotor?
How to know the back up time for a 5KVA UPS which is connected to 15 nos. of computers? Is there any formula for this? pls. tell me.
DIFFERNCE BETWEEN DCS AND PLC? HOW IT WORKS?
what are the standard transmision voltages in india?
What are the three major categories of error?
what are the main Parts of VCB
What will be MF for below rating ? Main CT PT value is 11kva/110 and 20/5 amp Meter display is 1kva/110v and -/5 amp What will be MF ? Multiplycity factor of energy meter
where is the primary of CT??
what is meant by dielectirc medium? what is the dielectirc value of air and water???
whati s the sludge current in ups
Why electrical engineer use Cu Strip for transformer neutral why not GI Strip? What if we use GI instead of Cu does it affects the transformer performance.
Is it possible to protect 3phase overload and earth fault of the 3phase system using two CT's.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)