why current coil has less number of turns compared to
pressure coil?
Answers were Sorted based on User's Feedback
Answer / vinod singh
current coil is connected in series so that its resistance
should be as minimum as possible otherwise there will be
voltage drop and power loss during normal working condition.
| Is This Answer Correct ? | 53 Yes | 6 No |
Answer / anindita
current coil is connected in series with the load whereas
pressure coil is connected parallel to the supply, that is
pressure coil is connected across the voltage source.
current coil have lesser number of turns than the pressure
coil so that the impedance of the pressure coil increases
and it draws minimum current from the circuit,causing lesser
error in the reading.
| Is This Answer Correct ? | 22 Yes | 6 No |
Answer / kundanmalani1990
bcz the CT are connected to the series in supply line so
that high current pass through the line and high current to
absorbers to CT so current coil has less number of turns
compared to pressure coil !!!!
| Is This Answer Correct ? | 12 Yes | 11 No |
Answer / ansuman
current coil have to measure current ; to achieve it less resistance is given by providing less number of turns in current coil.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / raju kumar
this is because,current supplied to the load may be more and more and wattmeter may get current reading of power supplied
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / raj kumar
Current coil connected in series with the load.in series circuit current is same and voltage different.if we are increasing the number of turns in the current coil as like pressure coil number of turns.
First load current only passes through the current coil because series circuit.so current increases automatically voltage drop will increase.so error will occur.it will not show the correct reading.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / nithi
IF CURRENT COIL IS PROVIDED WITH MORE NO. OF TURNS,THEN IT
WILL DROP MORE VOLTAGE ,AS IT IS CONNECTED IN SERIES WITH
THE LOAD.
| Is This Answer Correct ? | 7 Yes | 9 No |
Answer / mr. utsav jain
bcz current coil connected in series and the pressure of the current coil is very high so it will produce large voltage drops.
in parallel condition obtain the high voltage large no of turns.
| Is This Answer Correct ? | 2 Yes | 4 No |
why full load voltage is less than no load voltage?
Why we are using Isolation Power Transformer inplace of commercial power transformer? What's the difference between them?
What are the different protection systems takes place on control panel board?
Can Dy11 and Dy1 vector group transformers be paralleled?
IF HT CAPACITOR IN ON POSITION IS THERE ANY LOSSES I.S I SQURE OCCURS IN THE SYSTEM
What should be ideal IR value for 11kV, un earthed, 1 MW motor?
why we are using DC supply for all protection relays, why cant we use AC supply..???
what is the safety of voltage power transformer(2250KVA0
what is difference between KW and KVA
Hi friends. m 3 years drop. now d company asks in d interview d reason 4 my drop.what shud b d probable answers 4 that which may not put a negative impression.
What is power factor? How to improve Power factor? draw a circuit diagram showing the connection of power factor improvement equipment to the electrical instillation.
WHAT IS DIFFERENCE BETWEEN CAPACITOR AND CAPACITANCE?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)