where AVR is connected in power plant.
Answers were Sorted based on User's Feedback
Answer / ishwar shivanand dematti
RTCC Panel :-REMOT TAP CHANGING Control panel
Is This Answer Correct ? | 11 Yes | 3 No |
Answer / nitin bhoraokar , power plant
Yes. AVR is required for voltage regulation. AVR regulates
terminal voltage of generator automatically. Now-a-days
digital AVRs are preferred.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / k.prakashchandra
Excitation equipment which itself is called AVR or DVR In
old type, AVR was provided in control panel.
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / jeyapal
AVR is actually a PID Controller operating on a set point ,receiving a feed back sample of output voltage of an alternator and comparing with set point.Maintains output voltage and power factor by regulating the excitation level.Construction looks very simple in the form of a printed circuit board located just on the alternator or at times inside switch board panel with a cable run to the generator.
Is This Answer Correct ? | 0 Yes | 0 No |
3phase cable calculation formula by motor load
IN 500 KVA TRANSFORMER 11KV/415 VOLTS HOW TO CALCULATE THE HT CABLE SIZE AND LT CABLE SIZE FROM TRANSFORMER TO LT PANNEL. AND HOW MANY MAINSWITCHES OR MCBS WITH RATING ARE TO BE PROVIDED
explain Xmer
what do u mean by bus bar?
From what on-site components does the HT panel monitoring the bus-bars in a 11kV system take inputs?
Does outdoor isolator loose connection cause short circuit current in that circuit? if yes then how ??
What is the formula that shows relationship between voltage and speed in an induction motor
WHY HUMMING SOUND OCCURED IN HT TRANSMMISSION LINES?
how to crack cgpsc,which type of knowledge it is required,where i can get systematic study material and some tips?
How does MCB operate without relay..?
what is parellel power factor correction?
IF WE SELECT THE 60H FREQUENCY IN INDIA WHAT WILL THE GOOD AND BAD EFFECT ?