what is trip circuit supervision relay? How does it work in
switchgear?
Answers were Sorted based on User's Feedback
Answer / huzy
This relay continuously supervise the healthiness of tripping circuit.It gives an alarm for Open / short tripping coil or tripping supply failure.
| Is This Answer Correct ? | 44 Yes | 4 No |
Answer / raghavendran.r
I would like to add more on the previous answer.As stated
earlier trip circuit supervision relay will monitor the
proper functioning of trip circuits based on the feedback
signal obatained from the tripped circuit.if the circuit
has not tripped even after getting trip command,then as a
preventve measure sometimes LBB ie local breaker back up
will act upon to prevent any further damage to the system
due to any fault.
| Is This Answer Correct ? | 33 Yes | 5 No |
Answer / hanuman
trip circuit supervision relay is the relay which
supervises the trip circuit of the circuit breaker. It even
tests wheather dc supply to trip circuit is under proper
condition or not. some times trip circuit gives signal to
circuit breaker, but circuit breaker doesn't break the
circuit, then supervision relay makes circuit to break by
LBB.
| Is This Answer Correct ? | 19 Yes | 4 No |
Answer / k.prakashchandra
This relay is used to supervise the tripping circuit and to
provide alarm ,independent of breaker status, for 1)loss of
dc supply2)faults in trip coil or cables 3)faults on the
breaker aux contacts 4)faults in the relay itself
| Is This Answer Correct ? | 15 Yes | 5 No |
Answer / balaji
This Relay will monitor over All the tripping circuit's healthy condition and will provide alarm in tripping circuit unhealthy also Can be utilize multi level.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / nitin bhati
as its name indicate ...it works like a supervisor used to control the complete tripping circuit if there is a fault in controlling supply (dc) it sense it and gives a command to breaker.
| Is This Answer Correct ? | 2 Yes | 0 No |
what is the difference between 2 way and 4 pole selector switch???
if voltage in transmission line more than current will be more or less,if less what about the Ohm's law
How would you supply a single house hold load from a 3-phase supply coming out of a sub-station?
2. If 8.35%Z means the percentage impedance of 132/11kV transformer self,will like to reconfirm the percentage impedance that is supplied from power company?
State the difference between Surge Arrester and Lightning arrester,Both are same or not?
how to calculate a cable size while load is given in amp or kw and length is also define.?
why dc measurements are noted in mc whereas it is mi in ac measurements?
difference between high and low impedance BUS BAR relay??
What is the Impedance, inductive reactance calculations
What is the clear distance between a MV panel(rear side) and wall.
how to estimate wiring ins roughing ins. and boxes
We normally make oil soak pits under Transformers. Oil from soak pit goes to collection pit. We provide granules/pebbles under transformers. My question is weather granules/ pebbles to be filled in soak pit or not? if yes upto what level?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)