what is Bucholtz Relay test???? Explain??
Answers were Sorted based on User's Feedback
Bucholz relay can be tested in two ways
1. By shorting the terminals which is located in the
teriminal box of bucholz relay
2. This is real test to do this test you have to isolate
bucloz by closing the valve which is connected from main
tank to conservator tank there are two valves one is
entering to bulcoz relay and another is leaving from bulocz
relay these two valves to be closed and then there will be
a drain valve in bulcoz the bulcoz relay from there you
have to drain the oil then the float will come down it will
be activated.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / gaurang gurjar (c.i.t ,hanga)
bucholtz relay is only one protection device that is sence
the fault before occuring the fault.bucholtz relay provide
the transformer protection.bucholz relay place between the
consevator and transformer.
| Is This Answer Correct ? | 4 Yes | 5 No |
what is a panel board?
What is the difference between ACB & MCCB?
The knee point of a current transformer is normally unique and known.So why in the nameplate of a CT they put the minimum value like this Vk> 400v.
what is cascade speed control device?and how this device control the speed of motors?
what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ?
What are the difference between off-load tap changer and on-load tap changer in transformer?
What is the formula formula for Busbar sizing and what are the things to be consider for Busbar Calculation?
Why we are always only used 11 kv. , 22 kv ,33kv in transmission line? Why not use 25, 55 ,65 kv ?
3 Answers Khidmah LLC, Precision Camshafts Limited,
Need help. 3 phase system. Neutral line arced and melted upon connection of connector with 3 phase power. Why would that happen?
Technical requirement of Copper earthing over GI earthing.
If the load of transformer is getting more than its rating,,,than how to overcome this problem? Suppose thee rating of transformer is 315kva and the load is going beyond than the rating say around load: 352kva... Than how can we solve this problem without deducting the load.
What happened when a three phase induction motor work on two phase supply.9
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)