What is the difference between ACB & MCCB?
Answers were Sorted based on User's Feedback
Answer / j. a
Actually the ACB is abbreviation of Air circuit breaker,
which is normally used for LV switchgears and high current
(normally more than 400A). The switching contacts are
operating in the air. MCCB is abbreviation of moulded case
circuit breker which is normally used for switching of load
less than 630 A.
| Is This Answer Correct ? | 22 Yes | 0 No |
Answer / satya dev
As per IE Rule Below than 1000 Amp. Load we can use MCCB &
Above than 1000 Amp. Load we must be use ACB.another reason
is the Range of Short Ckt Capacity of ACB is Greater Than
the MCCB.
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / mahadikpramod
1)Differencfe between ACB & MCCB is mainly,ACB we can use
for large load and MCCB we can not.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / srabon1059
ACB(Air circuit breaker):
1.ACB provide over load,under voltage and short ckt protection.
2.mainly used in industrial are.
MCCB(oulded case circuit breker):
1.Provide over load ,short ckt protection.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / aravind
ACB :Air circuit breaker is available from 400A to 6300A .
They are generally used for O/L,S/C,E/f and metering
protection.
The breaking capacity is generally 35kA/50kA/60/75KA
MCCB:Moulded case circuit breaker is available from 32A to
1600A.
They offer all the protection as offered by ACB.
However MCCB are compact when compared to ACB for
respective ratings.
MCCB are difficult to repair and life is less when compared
to ACB.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mohammed yousuf khan
ACB stands for Air Circuit Breaker whereas MCCB stands for Moulded Case Circuit Breaker. Generally MCCBs are used for loads upto 630A but if the load is higher say beyond 630A then the ACBs are used.
1)Also ACB is long lasting when compared to MCCB.
2)The switching contacts of ACB operate in air, whereas the switching contacts of MCCB operate in a case. Hence the name ACB & MCCB.
3)Apart from Overload, Short Circuit & Earth fault protection, other protections such as Under voltage protection can be achieved using ACB.
4)MCCBs are very compact, whereas ACBs are large in size when compared to MCCBs.
5)MCCBs needs to be replaced after a certain operations but ACBs can be re-used with little maintenance, as the spares are easily available for ACBs such as Contacts,arc chute etc...
| Is This Answer Correct ? | 0 Yes | 0 No |
1. what is usage for power factor in industries?? 2.why we need to monitor power factor??
If SFU is Switch Fuse Unit, What is the expansion for FSHF in Electrical Engineering?
why trip circuit supervision is taking through breaker contact? what happen if takendirectly?
how does oil cools the transformer
1.Why sinle phase motor is not self starting 2.working principle of alternator 4.list out electrical formula
Dear all, I'm manikandan I have done by DIPLOMA EEE from 2011 , I have 5 years of experience from Power plant instrumentation field , which one field is give long life & which one field is best ,I confused a lot and also I'm studying AMIE, can I choose which department from Section B examination? pls tell me
how to read AWG n how to convert AWG reading into mm?
CORRECT INFORMATION ABOUT TRANSFORMERS,what actually transformer is?
orifice sizing how done, checking & selection
what is the difference between dropout fuse and horn gap fuse. how to choose between them
How vfd saving power.
when voltage increases current decreases & vice versa why it is so?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)