How can calculate ups battery back up time?
Answers were Sorted based on User's Feedback
Answer / g.shanmugam
Battery back up time=Battery current at full load/Battery Ah
| Is This Answer Correct ? | 308 Yes | 161 No |
Answer / guest
As a thump rule,if we need 1 hrs backup from the 1 KVA UPS
12V/130AH is Required,For Example,10 KVA ON-Line
UPS,Battery-12V/65AH,26 nos.
BAck-up Time=Ah of the Battery*Total no of the
Battery/Output KVA*130
BAck-up Time=65*26/10*130
BAck-up Time=1.3
BAck-up Time=60~70 Mins(Approx)
| Is This Answer Correct ? | 219 Yes | 147 No |
Answer / r.gopalakrishnan
SEE SUPPOSE IF I NEED 740 WATTS USAGE BACK UP TIME UP TO 3
HOURS, THAN I CAN CALCULATE LIKE THIS(EXAMPLE 1
PC@350WATTS,3 FANS@80X3=240WATTS& 3TUBE LIGHTS
@(40+10CHOKE)=50=150WATTS)TOTAL=740 WATTS REQUIRE,= 740
DIVIDED BY 12 V=(61.666667)>61 Ah per hourx3
ours=183Ahbattery,(180Ah Battery).now you have selected
battery & than select a UPS/inverter that is you can only
get 80% of your UPS/inverter.Ex;1000 watts Ups/inverter.that
will be always safe for you & ever.thanks.R.GOPALAKRISHNAN.
| Is This Answer Correct ? | 96 Yes | 40 No |
Answer / sss
UPS Backup=Battery Voltage*Battery Ah/Load (watt)
| Is This Answer Correct ? | 98 Yes | 47 No |
Answer / subir kumar manna
UPS BACKUP TIME= NO OF BATTERY X AH OF BATTERY /OUTPUT KVA
X130
| Is This Answer Correct ? | 66 Yes | 41 No |
Answer / parameshwara.s
Tell me on a 5 KVA UPS with 12 Batteries of 65 AH how many
hours of backup will I have on full load.
| Is This Answer Correct ? | 36 Yes | 11 No |
Answer / n.muthukumar
ups backup time=battery AH*battery efficiency*no.of
batteries/ups capacity in kva*130*output power factor
for example:65*0.9*10/5*130*0.8=1.125
approximately:1hr 15min
| Is This Answer Correct ? | 39 Yes | 21 No |
Answer / claudiu
You can calculate the max time to use a UPS with this
formula
T max = efectiv energi / average power of the energy
that min
T max = 1377 (this is a constant, it's so big because it's
calculate in seconds)* capacity of batery in volts 12V *
capacity of batery in amper's 10Ah or other valu * number
of moduls (number of bateris to use) / how mutch power you
want to consum in W
for exemple
I have 8 baterys with 12V and 10Ah and I want to standup a
computer with 300 W consum
so
1377*8*10*12/300 = 4406.4 seconds that min 4406.4/3600 =
1.2h
sorry for my english
best regards,
Claudiu from ROMANIA
The sours is
http://en.wikipedia.org/wiki/Uninterruptible_power_supply
| Is This Answer Correct ? | 29 Yes | 16 No |
Answer / asela
nomber of battery * battery voltage * each battery AHR
(130AHR total/ nomber of battery)130/260* efficiancy 90
PERCENT/ tatal VR.
26*12*5*0.9/1000
1 HR AND 4 MINUTES
| Is This Answer Correct ? | 38 Yes | 27 No |
Answer / yogesh
UPS backup time= Ah of battery * no of battery/output kva * 130
| Is This Answer Correct ? | 73 Yes | 68 No |
i have been tasked with a design of protection, metering and control(PMC) relay panel extension to accommodate all PMC relays.There is an already existing panel where this one will be built.What are the design aspects for this kind of project? thank you.
Can you any one explain different between instantaneous over current and IDMT
what is the tolerance for the magnetic balance test conducted on the distribution transformer?
what is the IS foe lightning arrester?
what is data block in plc ? How the values of data block are written and read by hmi ? what is the difference between function and function block ?
why occ characteristics curve in not tracing back when we are bringing back the rhoestat?
What is meant by transformer, why it should be used, with out that equipment what happens if we transformed the supply?
what is the contact resistance of vacume circuit breaker??
please send me RRB electrical engineer previous year questions for Sr. Section Engineer
we have two motors 1250kW,6.6kV to be coupled on the same shaft ,so please provide assistance for their synchronisation.
considering the 3phase and single phase ac system the load applied and the volage given is same...will the current differs for both the cases are it wil remain same?
in our transmisison sub station why we step down firstly 132kv\33kv then 33kv to 11kv. can we direct step down 132kv to 11kv.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)