how to calculate earth resistat in earthpit with earth
testing kit?
Answers were Sorted based on User's Feedback
Answer / thanigaivel
In that earth tester E1 and P1 short with wire and take a lead from that loop. and put 2 spike in that mother earth 1st spike connected to E2 and p2 connected to that another spike ... that looped wire is connected to earth bit . and put the earth test with ohms .. its show the value
Is This Answer Correct ? | 4 Yes | 0 No |
what are the duties of commutator in motor and generator?
What is difference between ct&pt transformers?
in the farm,water tank of 8000 litter capacity situated in 12 meter above.Farm owner want to lift 7000 litter of water within 7 minute to water tank of 12 meter above.which motor having HP rating is suitable for pumping??
1 Answers ABB, Anchor, Havells, Keltron, KSEB, L&T, vguard,
is the secondary voltage of current transformer greater than primary voltage,,,,,,,,] give the example with ct burden,current ratio,and primary and secondary side voltage?
What is center gravity load in substation?
What is the Difference between Power Swing and Out of Step?
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
How we calculate airgap between phases & terminal box of the transformer? any formulae.
How to calculate cable size for a particular load? i have 12 MW,11KV Motor 3 Phase, what should be cablesize? What are the points to remember for cable sizing calculations?
Why dose an electric meter record KVA when there is no load on a 500 KVA transformer
An 11kv system consisting of an underground cable to a sub station about 300 meters away was shut down for about 10 hrs. On energising, it tripped off on earth fault about 10---20 mins later 6 times but since than it is not tripping.its already 3 weeks now. The SPAJ was found to be fine. what could be the cause.No test had been done to determine the cause of the trippings till now because of demand.
what is the purpose of CT,PT