oil sample dielectric test gives the insulation rupture
voltage at 26 kv. is this transformer safe to be operated .
The working voltage is 11 kv
Answers were Sorted based on User's Feedback
Answer / sms
AS PER IS:6792 , Oil Electric break down voltage( BDV) at
room temp using 2.5 mm gap should be Min 30 KV .
Accordingly don't take risk and carry out oil filteration
as early as possible to avoid any break down.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / k.prakashchandra
40 KV is the minimum value required. You need not panic.
Measure the BDV again after 15 days. If there is drop ,oil
filtering is to be done at the earliest
Is This Answer Correct ? | 1 Yes | 1 No |
FOR WHICH FAULTS OR CONDITIONS DOES A TRANSFORMER DIFFERENTIAL PROTECTION DOES NOT OPERATE???
There are a trformer and an induction machine. Those two have the same supply. For which device the load current will be maximum? And why?
Dear sir, By which formula u can calculate for a particular kv line there is a range of mw.
A heater capacity is 3.0 KW on 415V . if supply voltage is 380Volt . what is heater capacity on 380volt . and how calculate and give formulas . Prakash veer singh Roto power Engg.
what is use of mccb.
When in a large power system if the demand of power is larger than the generated power the frequency of the power system drops.(assume the rated frequency is 50Hz and now it is 49Hz) So does this mean the demand is totally supplied with a lower value of generated power in a lower frequency?
what is ACB
How to calculate & connection of 900KVA generator 2 sets & load(1500A)? How to choose cable size and ACB size for this load & generator? please explain me detail. Regards, Mr.Han
what is dead tank CT AND what is live tank CT
what is T P N bus bar
what are the problems that generally occur in power flows??
if we have to design a small transformer of rating 1 kva or 1 mva , how can we design it?