oil sample dielectric test gives the insulation rupture
voltage at 26 kv. is this transformer safe to be operated .
The working voltage is 11 kv
Answers were Sorted based on User's Feedback
Answer / sms
AS PER IS:6792 , Oil Electric break down voltage( BDV) at
room temp using 2.5 mm gap should be Min 30 KV .
Accordingly don't take risk and carry out oil filteration
as early as possible to avoid any break down.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / k.prakashchandra
40 KV is the minimum value required. You need not panic.
Measure the BDV again after 15 days. If there is drop ,oil
filtering is to be done at the earliest
| Is This Answer Correct ? | 1 Yes | 1 No |
why the earth conductor in top of the tranmission line ?
what is the function of choke in tube
Motor also having losses, we call KW rating. In transformer and generator having losses but we call KVA Rating why?
how to calculate the torque of a motor?
if we use contactor & MCCB both in a feeder.in this feeder rating of contactor is higher or lower or same of MCCB rating & why?
what are the alternator cooling system? how it is represented?
what is the function of avr when synchronous generator act as synchronous motor
whata is battery charger ?how many cells connected for 110v?
What are books to be referred for KPTCL exam?
What is ERD used in Elevators??
how can decide the current rating of oltc
What is fuction of NGT/NGR using in Generator.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)