What is the method & formula of Fault level calculation in
power Transformesr.
Answers were Sorted based on User's Feedback
Answer / dinesh
since %impedance is the per unit value, u can get the short circuit fault current level by,
Ifault = Irated (phase current) / %z..
Similar method if u need fault level MVA....
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / k.prakashchandra
% impedance( Say P )= I rated x Z x 100 /V rated. Hence Z =
P x Vr /Ir x 100. Fault current If = Vr /Z .Then If= Ir x100/P
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
I think you have to multiply by 100 ,in the above answer as
otherwise the fault current will be less than the rated.
| Is This Answer Correct ? | 1 Yes | 0 No |
Mention how NPN and PNP transistor works?
what is difference between KW and KVA
haw to calculate resistance of induction motar
defination of loads
What is RMU, and what it's function?
how electronic energy meter works?
In VSD (variable speed drive)I/P and O/P connections given wrongly what will happen?
How many types of DC current
What is the need of motor starter?
In power transmission using open belts or horizontal shafts it is preferable to have the slack side of the belt on the top because
Why r used of cable 50sq.mm and above size cable in 3.5 core. And below size in 4 core ? any technical reason please explain it
What are the different parts of Alternator and how it works?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)