when neutral will carry the current?what could be the
magnitude?
Answers were Sorted based on User's Feedback
Answer / ajay patel
In case of SIngle Phase System Neutral will carry current
of same magnituge as phase current.
In case of 3 Phase, Star Connected System, neutral will
carry current only during unbalanced or Phase to Neutral
fault condition. During balanced condition current through
neutral is zero(Ia+Ib+Ic=0). In case of Unbalance load
Neutral Current can be maximum as phase current. & In case
of Phase to Neutral Fault Magnitude of neutral current will
be same as fault current. In case of Phase to Earth Fault,
neutral current will be 0. Earth current is suppose to pass
through Earthing grid or Armoure of cable.
| Is This Answer Correct ? | 14 Yes | 4 No |
Answer / satish panchal
Nuetral will carry current in unbalance & faulty / EF or SC
condition. During normal condition vector sum is Zero and
megnitude is also zero, but in faulty condition zero
sequence current will flow through neutral and megnitude
depends upon fault strenght.
| Is This Answer Correct ? | 8 Yes | 0 No |
As per KCL Sum Of Individual Current is Equal to Zero.
That's the Neutral Point is Zero.
In Unbalnce Condition the current will flow in neutral
point. that magnitude will Based on Faulty Current.
Balanced Condition Ia+Ib+Ic=0(N)
Unbalanced Condition Ib+Ic=-Ia(N)Faulty System only.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / vasim
In normal condition there will not be any current in
Neutral, and the vector sum will be 0, If there is any
EF/SC/Unbalance occured the fault current will always pass
through the lowest resistance path in this case neutral is
the lowest resistance path so when neutral will caryy the
load the magnitude will be equal to the magnitude of fault
current...
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / orlando rodriguez orense
Neutral conductor are not normally design to have current.
However neutral conductor is installed to be the escape way
of electrical fault and thus a electrical safety features.
The magnitude of the current therefore will be the size of
the fault and in case of negative voltage sequence occurence
cause the neutral conductor to carry that magnitude.
| Is This Answer Correct ? | 3 Yes | 3 No |
What is the full name of one of choke less lamp BLL
Which types of following motors are most efficient?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
how many types erthig
For 160kw motor what size of cable and material is needed.?
What are all present producing cost of Per KWH of various Fuel?
can we light the mercury vapour (tube light)with out a 1).starter and 2).choke in our homes if yes explain how?
Why is making current of CB always greater than CB breaking burrent?.
what is the lemen of a single 5mm 13000mcd white led pls reply
What difference between voltage and current
does over charging of a battery reduce its life?
CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)