Answer / ajay patel
In case of SIngle Phase System Neutral will carry current
of same magnituge as phase current.
In case of 3 Phase, Star Connected System, neutral will
carry current only during unbalanced or Phase to Neutral
fault condition. During balanced condition current through
neutral is zero(Ia+Ib+Ic=0). In case of Unbalance load
Neutral Current can be maximum as phase current. & In case
of Phase to Neutral Fault Magnitude of neutral current will
be same as fault current. In case of Phase to Earth Fault,
neutral current will be 0. Earth current is suppose to pass
through Earthing grid or Armoure of cable.
Is This Answer Correct ? | 14 Yes | 4 No |
Answer / satish panchal
Nuetral will carry current in unbalance & faulty / EF or SC
condition. During normal condition vector sum is Zero and
megnitude is also zero, but in faulty condition zero
sequence current will flow through neutral and megnitude
depends upon fault strenght.
Is This Answer Correct ? | 8 Yes | 0 No |
As per KCL Sum Of Individual Current is Equal to Zero.
That's the Neutral Point is Zero.
In Unbalnce Condition the current will flow in neutral
point. that magnitude will Based on Faulty Current.
Balanced Condition Ia+Ib+Ic=0(N)
Unbalanced Condition Ib+Ic=-Ia(N)Faulty System only.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / vasim
In normal condition there will not be any current in
Neutral, and the vector sum will be 0, If there is any
EF/SC/Unbalance occured the fault current will always pass
through the lowest resistance path in this case neutral is
the lowest resistance path so when neutral will caryy the
load the magnitude will be equal to the magnitude of fault
current...
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / orlando rodriguez orense
Neutral conductor are not normally design to have current.
However neutral conductor is installed to be the escape way
of electrical fault and thus a electrical safety features.
The magnitude of the current therefore will be the size of
the fault and in case of negative voltage sequence occurence
cause the neutral conductor to carry that magnitude.
Is This Answer Correct ? | 3 Yes | 3 No |
How I calculate the ELCB for circuit breakers?
why current is denoted by I
What is the starting current of a DC Motor?
WHY CFL can't made in shape of bulb.
I Have 3 Phase 10 KW AC Alternator i found one phase weak, so what will be the reason & what action shouls i take to rectify the same.
what's the difference between ATS and AMF...??pls answer me in detail with its working principle and construction also..
if harmonics is generates on the secondary side of transformer then why we put LC ckt on prim side?(i m talking abt rectiformer transformer)
FOR WHICH FAULTS OR CONDITIONS DOES A TRANSFORMER DIFFERENTIAL PROTECTION DOES NOT OPERATE???
we use capister for power factor. when we use capaciter in dg circuit than defect dg. can we use capaciter bank for dg circuit
Define Current Transformer? Working & TYpe's Of C.T.
How do you select a cable size(Cu&Al) for a particular load
10 Answers Adhunik, BPCL Bharat Petroleum, Hiecon, TATA,
on a three-winding transformer relationship delta-delta-star, on third winding why the relationship is a star? what are the advantages and disadvantages? Thank you and please help