Explain role of Buckolz Relay in Transformer ?
Answers were Sorted based on User's Feedback
Answer / niloy
Buckolz Relay is connected between transformer tank and
conservator.It gives protection from mainly over
heating.The overheating can be done by any way-- by
sparking or by short circuit or by any internal fault.When
transformer oil overheated it decomposes itself and create
some hydrocarbon and produce hydrogen gas.. This light
weight hydrogen gas moves to the upward direction and trap
into the buckolz relay.After collecting a sufficient
ammount of gas the buckolz relay give a alarm signal and
trip the breaker to protect the transformer to getting
damaged from over heating.
We can collect the gas stored in the buckolz relay and can
analyse it to know the types of fault.In big transformer a
gas holder is connected to the buckolz relay to collect the
gas..
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / tango
Buchholz Relay is a gas actuated relay installed in the oil
immersed transformer for the protection against all kind of
faults. It is used to give an alarm in case of slow
developing faults in the transformer and to disconnect the
transformer from the supply in the event of severe internal
faults, always used for transformer having rating exceeding
75 kVA.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / pillay
I wish to add to TANGOS answer.When faults due to insulation breakdown,sparks within the windings or due to insulating oils
properties breakdown which may cause the developments of air within the transformer.This air bubble is used to activate the
BUCKHOLZ relay and trip off the transformer.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / anil
Buchholz Relay is a gas actuated relay. The main advantage of this relay when compared to other type is, it will give alaram
Before,in the case of internal fault. That means a operator can take the preventive means and he can operate,other wise it will trip automatically.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pillay
Thanks mr sharma.It should had been gas instead of air in my answer but I didnt know it was hydrogen gas.Thanks again.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ravinder sharma
sorry pillay sir this is not air ,this is hydrogen gas .
| Is This Answer Correct ? | 2 Yes | 2 No |
the winding of Gen and Motor is star or in delta ??? and why
What is the difference between Generator Differential Relay and Transformer Differential Relay?
what is neutral voltage
Why does the rotor rotate?
1 Answers Machino Polymers, OPTCL,
how many earthing should give for transformer body and nuetral
Draw SLD for a panel has 500A Bus Bar rating, with 4 outgoing, each is 80 A (load current), showing the transformer and capacitor bank rating.
Conventionally, capacitors are considered to generate reactive power and inductors to consume it,how??????
what kind of motor is used for lifting applications
Why the bypass and blocking diodes are used in solar modules?
How much inductance or resistance require as a starter in series with induction motor of specific capacity(e.g. 5 hp) ? What is formula for it ?
why we have to particulary use ACB for below ratings,even available of MCB,MCCB with that range ?
2 Answers QRG Health City, Siemens,
what is S.D.F stands for ? (S.D.F unit 80 amp , TPN )
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)