if voltage is not builed up in small generator what will be
the reason?
Answers were Sorted based on User's Feedback
Answer / nimish
there are so many reasons there may not be a residual
magnetism in d.c. generator then if critical resistance is
more than field resistance
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / j.kesavan
some times diodes failur in exciters,thats why voltage not
built in gen set
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / swayanjit
if voltage build up is not possible then there may be open
circuit in the field or armature, may be due to dirty
commutator, may be the speed less than the critical spped,
may be the field resistance greater than the critical
resistance.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / shakir
there are so many reasons:
1.the exciter might have problem
2.the ac produced in exciter is converted into dc before
supplying it to the rotor.the diodes used for this purpose
might have problem.
3.when u start the generator there should be a residual
magnetism to induse the voltage.if u will not use the
generator for long time, it will loose that residual
magnetism.for that purpose u have to give flash over
voltage.
4. the exciter winding might be grounded.
5. the input (D.C.from voltage regulator)voltage to the
exciter is not enough to create flux in the exciter.
6.faulty stator winding
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sirisha
it is because the polarities of the field windings are
reversed.
| Is This Answer Correct ? | 4 Yes | 3 No |
Does the total power means fundamental plus Harmonics?
what is the control circuit for operating the clean room air shower
v=I*R, i.e V is directly proportional to I. now P=V*I. so V=P/I. thus v is inversely proportional to I. so what is the correct one? If both are correct than for which kind of condition this 2 differ
why full load voltage is less than no load voltage?
the 230 value of voltage which is use in our home . is that value is rms, aerage or peack value of voltage?
What is the required bending radius requied at the time of cable laying?
1.4 What is meant by CT knee point voltage and how would you determine it
what is the pressure of vacuum circuit breaker
What the main causes of transient interruptions on Over-Head Distribution Lines?
How to calculate the cable size (XLPE)for suitable to 120KW load (if Motor or heaters etc)
For some transformers we are using solid neutral earthing while some others we are using resistance earthing why ?
what is transformer?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)