how to calculate the multiplying factor for energy meter
with CT ratio given
Answers were Sorted based on User's Feedback
Answer / reshma agrawalla
Multiplying factor=connected CT ratio/meter CT ratio*connected PT ratio/meter pt ratio*scale factor
Scale factor=1(for kwh meter)
Scale factor=1000(for mwh meter)
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / avinash pawar
MF = Main PT ratio × Main CT ratio / Meter PT ratio
Main PT ratio = 22kv / 110v
Main CT ratio = 400 / 5
Meter PT ratio = 11kv / 110v
So, MF = { 22000/110×400×5 } /11000/110
MF = 160
| Is This Answer Correct ? | 0 Yes | 2 No |
what causes contact chatter when there is no demand on the air conditioning unit?
How to Prepare preventive maintenance shedule of machine tool.
Distinguish between neutral earthing and equipment earthing?
why odd hormonics only will effect the power system.why not even hormonics
What is the difference between grounding & earthing?
What are the effects to a distribution transformer rated 10Kv with ratio 10Kv/0.433Kv, 3phase 50hz for example but fed with power supply of 11Kv?
what is the difference between b c d curves on mcb
is there any difference in reading or error in value, if we connect the R phase in Y terminal and Y phase in R terminal of electronic energy meter of 11 kv feerders???
What is PCCB?
WHY IS THE UNITY POWER FACTOR NOT THE MOST CONOMICAL POWER FACTOR?
What is current and voltage?
Batteries. What is the difference between Lead and Nickel batteries ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)