what is the difference between Resin Cast CT and Oil cooled
CT?
Resin Cast CT and PTs are usually used in indoor
switchgeear 11kv or 6.6kv substations etc. whereas Oil
cooled CTs are used in outdoor substations viz 11kv or 33kv
switchyards.
Difference is that Resin cast are solid cast type. Oil
cooled are those immeresed in Transformer oil and sealed.
In larger capacity CTs where cooling is required then oil
cooled CTs are preferred.
| Is This Answer Correct ? | 10 Yes | 0 No |
how dg's working of 1000kva.
what is the purpose of %impedance for transformer
Explain the construction of the conservator, operation and purpose, and draw the diagram of the conservator.
What is the "IS" for Rising Main?
What is the maximum current carrying capacity for both copper and aluminium cables for 1sqmm?
i have 2kv ups how many watts batteries is required
what is the ka rating of mccb. and how it is decided .
I have running 4 generator in paralel.All generators Voltages is same(470 V),KW also same (100 KW) but only No2 generator Amper is high than another generators. DG No:1,3,4 470V,100KW, 150 A DG No:2 470V,100KW,400 A
expansion of rccb
MCB MCCB ACB VCB
why the making current is more than then the breaking current and if its true then its about a controling circuit or breaker power contact points
what do you mean by mf of energy meter & its formula?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)