Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate battery back up time for a 400 AH battery
bank installed in telecom shelter for a load of 20 Amps and
time taken to fully charge this battery bank?

Answers were Sorted based on User's Feedback



How to calculate battery back up time for a 400 AH battery bank installed in telecom shelter for a..

Answer / pavan

Part -I:

400Ah Battery means the battery can supply a DC load of 400
Amps for a duration of 1 Hour until the battery gets fully
discharged. so if you are using the battery to supply the
above mentioned load of 20 Amps the battery can work for
400/20 = 20 Hours. provided the 20Amps is a Direct load
connected to the Battery. if you use the battery for a
inverter or UPS to suplly an AC load of 20 Amps. then the
duration is different.

Part - II:

For charging any battery we have to provide a voltage that
is slightly (5% - 10%) higher than the Battery terminal
voltage. The duration of charging can be known by the same
process as above. A 400Ah gets charged in 1 Hour provided
the charging source is capable of supplying 400 Amps to the
Battery. But normally the current of the charging source
will be limited to a lesser finite value. so if you can
know the maximum load the source can supply you can easily
calculate the duration required for the battery to get
fully charged.

Is This Answer Correct ?    27 Yes 5 No

How to calculate battery back up time for a 400 AH battery bank installed in telecom shelter for a..

Answer / dharmendra kumar gautam

20hours for fully charged of 400ah battery bank

Is This Answer Correct ?    12 Yes 2 No

How to calculate battery back up time for a 400 AH battery bank installed in telecom shelter for a..

Answer / suyog

if we connected many cells (24) of 200Ah then how i calculate its back up for 10Amp load

Is This Answer Correct ?    3 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what do you mean by puncturing of insulator by ice -coating?

2 Answers  


If I want to buy a new Xformer for my plant what are the main parameter will I need to check?

0 Answers  


Practical condition in 400KV Sub station:- Breaker(open) , isolator(open), Earthing (close) at both end e.g A & B. Now Open A Stn Earthing than Open B stn Earthing (Which have a 50MVA reactor) , AND suddenly show R,Y,B phase 704KV,573KV,118KV respectively. Que is without closing of breaker how it is possible.???? My Whats app No:07621840498 for Further Discussion. Pls experts suggest.

0 Answers  


how to find the transformer effiiency

3 Answers   Bosch,


What is the minimum percentage of power that a powerplant can support in ilanding mode ?

1 Answers  


what is allowable current flows from phase to ground with out tripping the breaker

1 Answers  


why inductancce of armature inductance of dc machines is neglected?

2 Answers   APPSC,


how we decide wire gauge for ac or dc coil and what is the basic diff. B/w these two coil?

0 Answers  


what should be the megger test report for 11KV cable when meggered with 5KV megger , what is the resistance value we should get

7 Answers  


what is difrent between earthing and ground

4 Answers  


WHAT IS DEGREE OF COMPOUNDING IN D.C MACHINE MEANS? HOW TO READ THE OPERATING CHART FOR ANY ELECTRICAL MACHINES?

0 Answers   Coal India, Ghana Grid Company,


how to calculate the MF in meter reading

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)