Part -I:
400Ah Battery means the battery can supply a DC load of 400
Amps for a duration of 1 Hour until the battery gets fully
discharged. so if you are using the battery to supply the
above mentioned load of 20 Amps the battery can work for
400/20 = 20 Hours. provided the 20Amps is a Direct load
connected to the Battery. if you use the battery for a
inverter or UPS to suplly an AC load of 20 Amps. then the
duration is different.
Part - II:
For charging any battery we have to provide a voltage that
is slightly (5% - 10%) higher than the Battery terminal
voltage. The duration of charging can be known by the same
process as above. A 400Ah gets charged in 1 Hour provided
the charging source is capable of supplying 400 Amps to the
Battery. But normally the current of the charging source
will be limited to a lesser finite value. so if you can
know the maximum load the source can supply you can easily
calculate the duration required for the battery to get
fully charged.
| Is This Answer Correct ? | 27 Yes | 5 No |
Answer / dharmendra kumar gautam
20hours for fully charged of 400ah battery bank
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / suyog
if we connected many cells (24) of 200Ah then how i calculate its back up for 10Amp load
| Is This Answer Correct ? | 3 Yes | 0 No |
what do you mean by puncturing of insulator by ice -coating?
If I want to buy a new Xformer for my plant what are the main parameter will I need to check?
Practical condition in 400KV Sub station:- Breaker(open) , isolator(open), Earthing (close) at both end e.g A & B. Now Open A Stn Earthing than Open B stn Earthing (Which have a 50MVA reactor) , AND suddenly show R,Y,B phase 704KV,573KV,118KV respectively. Que is without closing of breaker how it is possible.???? My Whats app No:07621840498 for Further Discussion. Pls experts suggest.
how to find the transformer effiiency
What is the minimum percentage of power that a powerplant can support in ilanding mode ?
what is allowable current flows from phase to ground with out tripping the breaker
why inductancce of armature inductance of dc machines is neglected?
how we decide wire gauge for ac or dc coil and what is the basic diff. B/w these two coil?
what should be the megger test report for 11KV cable when meggered with 5KV megger , what is the resistance value we should get
what is difrent between earthing and ground
WHAT IS DEGREE OF COMPOUNDING IN D.C MACHINE MEANS? HOW TO READ THE OPERATING CHART FOR ANY ELECTRICAL MACHINES?
0 Answers Coal India, Ghana Grid Company,
how to calculate the MF in meter reading
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)