Part -I:
400Ah Battery means the battery can supply a DC load of 400
Amps for a duration of 1 Hour until the battery gets fully
discharged. so if you are using the battery to supply the
above mentioned load of 20 Amps the battery can work for
400/20 = 20 Hours. provided the 20Amps is a Direct load
connected to the Battery. if you use the battery for a
inverter or UPS to suplly an AC load of 20 Amps. then the
duration is different.
Part - II:
For charging any battery we have to provide a voltage that
is slightly (5% - 10%) higher than the Battery terminal
voltage. The duration of charging can be known by the same
process as above. A 400Ah gets charged in 1 Hour provided
the charging source is capable of supplying 400 Amps to the
Battery. But normally the current of the charging source
will be limited to a lesser finite value. so if you can
know the maximum load the source can supply you can easily
calculate the duration required for the battery to get
fully charged.
Is This Answer Correct ? | 27 Yes | 5 No |
Answer / dharmendra kumar gautam
20hours for fully charged of 400ah battery bank
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / suyog
if we connected many cells (24) of 200Ah then how i calculate its back up for 10Amp load
Is This Answer Correct ? | 3 Yes | 0 No |
What do you mean by passive circuit elements and why these are called passive?
During regenerative breaking= A rotating magnetic field is reversed B slip is positive C torque is positive D slip is negative
How to get Electrical Supervisory Licence in chennai Tamil Nadu from TNEB. I am BE EEE graduate.
what is the harmonics? which harmonics(fundamental and reference) is suitable for calculating capacitor bank and Active filter and passive filter? what is the 1st 2nd 3rd 4th 5th harmonics and effects?
In directional earth fault protection for generator, one core balance CT is for residual current, what other CT is for, which is placed on neutral?
what happend if we remove dc exciter from moving machine..: gg
why the blede and jow of isoletor demage in substation?explan.
a transformer runs by electro-induction principle like all motors.then why dosen't it rotate just like any other motor
I am an electrical power engineer and arranged power system for a data center, I installed MCB, ELCB and erthing system TN-C-S. But some times several ELCBs Disconnect circuits at the same time! what may be the reason? (the ELCBs are 25A ,30mA)
Why Lightning arrester used? Can we use piece of iron as a core material of transformer, if No, why? In CRGOSS material what is meaning of cold rolled grain oriented? Why Impegrenation of Transformer is done? Properties of Insulator? what is phase angle? Testing of transformers (Routine & Monthly)?
Hi, I'm going to attend BHEL interview for exexutive trainee (ET ) on 22nd DEC . Till now if anyone attended the interview pls help me out regarding the interview. I'm an electrical engineer
Technical equations