Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate the NGR value for a 2.7MVA Transfomer,
11KV system where the fault current has to be limited to
50A?



How to calculate the NGR value for a 2.7MVA Transfomer, 11KV system where the fault current has to..

Answer / pavan

The value of the NGR to be inserted in the cicuit can be
calculated by the simple formula

R = V / (&#8730;3 * I)

Where V is the System Line voltage in Volts
I is the value of the fault current to be limited in your
case it is 50A.

In general practice the fault current is limited to the
full load rating of the largest equipment available in the
system.

Is This Answer Correct ?    6 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

what's the difference between 'shaft power demand' and 'BHP' , when we consider electrical load list.

0 Answers   HEC,


which signal we found accurate reading of analog signal or degital signal and why?

1 Answers  


What is the difference between KW & KVA ?

9 Answers  


Fantio of tranformer

0 Answers   Tenon,


Why is it that polarization index type test is required for MV and HV motors and not for LV motors?

3 Answers   La-Gajjar Machineries, Qatar Airlines,


why we are using DC supply for all protection relays, why cant we use AC supply..???

1 Answers  


what is meaning of bus raiser???

1 Answers  


What will be the size of cable required for 5.5 KW motor ( Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.

2 Answers  


HOW to speed control of induction mototr using scalar control

3 Answers  


in a distribution board,if we have a load and we have selected a cable after making all calcs (Deratings and V.D , ect...) the cable we have selected was 10mm.sq. now, shall the internal cable inside the switchboard should be 10 mm.sq Like the external or it can be Less???? if somebody have an specs or information he can help D:

1 Answers  


in pf lagging means current decrease by increasing voltage is correct or not ? reason ?

3 Answers  


Which is the largest hydropower station in the world?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)